This subject has been discussed alot online and has more than a few angles; but can someone tell me if this sounds right:-
TNC-S system's are not favoured (by the DNO'S) to be exported outside the equipotential zone (EPZ), because:-
1. (Consider here the TNCS has been exported outside the EPZ). If there's a break in the supply neutral (also earth), which coincides with a fault in an outbuilding (a short to metal casing) then there exists a potential (risk) to true earth.
2. If a similar fault happened indoors (within the EPZ), the potential to true earth would not be present ??
If the 2nd example is correct, then does that mean all the time you standing in the house (within the EPZ) there can be no possibility of a fault current travelling through your person (via the flooring) to earth. Bear in mind that all bonding would be rendered useless as there is no path for it due to the broken neutral; so would that mean any live extraneous parts would remain potentially static until the neutral were reconnected.
The problem im having with the second example is; any extraneous parts directly connected directly to earth within the EPZ (structural steels for example), would have just as much capacity to carry fault currents to earth as it would be outside the EPZ.
Discuss
Cheers
TNC-S system's are not favoured (by the DNO'S) to be exported outside the equipotential zone (EPZ), because:-
1. (Consider here the TNCS has been exported outside the EPZ). If there's a break in the supply neutral (also earth), which coincides with a fault in an outbuilding (a short to metal casing) then there exists a potential (risk) to true earth.
2. If a similar fault happened indoors (within the EPZ), the potential to true earth would not be present ??
If the 2nd example is correct, then does that mean all the time you standing in the house (within the EPZ) there can be no possibility of a fault current travelling through your person (via the flooring) to earth. Bear in mind that all bonding would be rendered useless as there is no path for it due to the broken neutral; so would that mean any live extraneous parts would remain potentially static until the neutral were reconnected.
The problem im having with the second example is; any extraneous parts directly connected directly to earth within the EPZ (structural steels for example), would have just as much capacity to carry fault currents to earth as it would be outside the EPZ.