krisbel

Ive got a job on wiring a new 2 story extension. it will require new ring final circuit, shower and cooker at least. possibly a lighting circuit. the tenant does not want the original mains unit changing but it isn't up to date. am i able to install a new consumer unit for the new circuits so not to disrupt the old one and run it as a sub-mains.
all advice greatly received

 
put another rcd board or rcbos next to old board, keep all your install separate from the old **** and dont forget you will need smoke detectors linked from hall to landing as a minimum building reg
 
yeah i know about the smokes. thanks for the advice. should i just split the tails into emery blocks then???

- - - Updated - - -

and as for certification would it just need testing on the new install??
 
Yes to both , you are not responsible for the existing installation as long as your new board , installation and earthing comply to the current regulations. If you were to tap into the old install you would have to comply with certain measures.

PS . But you will of course bring any faults to their attention as any responsible person would.
 
Yes to both , you are not responsible for the existing installation as long as your new board , installation and earthing comply to the current regulations. If you were to tap into the old install you would have to comply with certain measures.

PS . But you will of course bring any faults to their attention as any responsible person would.

of course. I want to do the lot as it would tie me over with more work in these tough times
 
yep, henly block it ( not emery, that's for close shaving yer face) from meter into separate CU. then you're only responsible for the new work. obviously, both old and new boards would have common eartrhing asnd bonding, so you'd have to ensure they were up to spec.
 
le
slightly worried about the kind of questions the OP is asking...


Well there is so much misinformation out there , he may just want a bit of clarification. Lots of people on forums think they are responsible for the whole install . it's the folklore born out of courses amongst other things. Go to any wholesaler and listen to the garbage spouted.
 
le


Well there is so much misinformation out there , he may just want a bit of clarification. Lots of people on forums think they are responsible for the whole install . it's the folklore born out of courses amongst other things. Go to any wholesaler and listen to the garbage spouted.

+1 very true
 
These idiots never cease to amaze me, willing to spend 10's of thousands on a new extension, but baulks at the cost of two or three hundred, for an updated CU, and keeping his family safe!!
 
Last edited by a moderator:
Same folk who queue for 6 hours for Takethat tickets yet miss the opportunity to get their kids vaccinated :bucktooth:
 
le


Well there is so much misinformation out there , he may just want a bit of clarification. Lots of people on forums think they are responsible for the whole install . it's the folklore born out of courses amongst other things. Go to any wholesaler and listen to the garbage spouted.

That is exactly it. I'm new to signing off my own work so was just after some advice. Better to ask someone who knows than take a punt. After all it's why these places exist! Thanks for your help Ruston
 
as has been said.....split the tails off into phase blocks...
get yoursen a Ze before starting............
you are responsible for the work you do.....
 