I needs to install 7 external bulkhead lights, but I could do with a steer on bringing the cable into the light - see below
4158B045-4130-466C-8F30-45AD6D00DDE4.jpeg


The glass which came with it are crap, the unit is threaded for 20mm so I can soon get these.

Depending on location I have one or two T&E coming in - standard flat grey.

Questions-
1. Would the gland seal ok on the T&E?
2. As it is “side” entry rather then rear, what do I do about the exposed T&E coming out of the wall?
3. Any advice on the what to do with the exposed hole - see below.

Any advice would be greatly appreciated

Thanks

0BA4E61D-4AFB-448B-B492-EEC55DE3BB18.jpeg
 
You can get glands which accept pairs of cables, your biggest problem is the cables being exposed to the elements. You may have to fit a joint box to enclose them and suitably connect from there.
 