Hi all just a quick question, I was asked to have a look at an electric shower today that keeps tripping the breaker, ive also been told that the pull cord switch in the bathroom has previously been replaced on 3 or 4 occasions. the owner of the house said it tripped the breaker last night and when he attempted to switch back on noticed that the breaker was red hot so left it off. IR tests didn't show any issues and visual inspection of breaker, switch and terminal block in shower didn't highlight anything either, so im wondering if its the shower itself or the internal parts of the breaker that's faulty, does anyone have any thoughts on this?
 
noticed that the breaker was red hot........so im wondering if its the shower itself or the internal parts of the breaker that's faulty, does anyone have any thoughts on this?

Are you qualified to be working on electrical installations? What did you IR test, the circuit or just the shower? What other tests did you do and what results did you get?

Even if the shower is faulty it wouldn't cause the MCB to get 'red hot'. It's also highly unlikely it's the 'internal parts of the breaker'. I'd be checking the external parts to start with, you can prove if it's internal by checking volt drop across it.
 
i don't think the breaker was belting out 800 degrees centigrade. i think the op was using a bit of hyperbole.
 
Clamp your probes into the MCB itself and check for continuity... Anything more than zero (or there abouts!) then it could be at fault...
 
check the wattage. some DIY dave may have fitted a 10kW shower on a 32A MCB. if you can get the MCB to hold, measure the current with a clamp meter.
 
Thanks for the replies, I checked continuity across the breaker and 0.04 ohms and once the cover of the shower was off I found a label stating it is a 7kw shower. Ive put a clamp meter round the live and most of the time got a reading of around 28.8a which is what ild expect from 7kw. every couple of minutes it did drop to around 12a and the water temp would drop. im now sure its the shower at fault as its not keeping a constant temperature. I was unable to get it to repeat the fault of tripping breaker but combined with all tests on wiring giving good results and the changes in water temp/current being drawn ild say a new shower is needed. whats other peoples thoughts?
 