In a house where i'm working at the minute (looking for a ghost thats tripping the RCD) I noticed theres an electric towel rail in the bathroom, the and theres an unswitched FCU (with flex outlet to the towel rail) below said rail about a foot away from the bath. in the next room theres a switched FCU on the ring that feeds this.
obviously it's not allowed, but how do i go about rectifying this? is there such thing as an IP55 flex outlet to fit onto a recessed backbox?? or do i tell them i'm gonna have to disconnect it? is an electric towel rail even allowed inside zone 2?
also in the same bathroom theres also another switched FCU even closer to the bath, connected to something that blows bubbles into the bath!! never seen one of these myself, and the tennants say they will never use it so i disconnected it. the FCU is directly on the ring, so at the minute i've just put a blank plate on it as i can't getird of it completely without breaking the ring. whats the score with this? i'm not keen on live stuff on a 32 a breaker at the foot of the bath, looks like an accident waiting to happen!
 
yes towel rails are suitable for zone 2 , nearly all of them are IP44
putting blank plate over unused spur is fine , no need to do anymore.
change towel rail spur to just a standard flex outlet as its switched from another room.
simples.
 
It seems odd that there's 2 FCU's for the towel rail. I lie, it's not odd, nothing surprises me anymore...
 
yes towel rails are suitable for zone 2 , nearly all of them are IP44
putting blank plate over unused spur is fine , no need to do anymore.
change towel rail spur to just a standard flex outlet as its switched from another room.
simples.
OSG table 8.1 says "min degree protection IPX4 (5 if water jets) fixed permanently connected equipment allowed. general rules apply" thing that i was bothered about is a standard white plastic accessory isn't IPX5, is it just the current using equipment the regs are bothered about?

It seems odd that there's 2 FCU's for the towel rail. I lie, it's not odd, nothing surprises me anymore...
must have ran out of flex outlet plates and just stuck an FCU in!
 

Reply to FCU inside zone 2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Replies
1
Views
1K
Hi all, Got an antique light fitting that for some reason she wants putting up (can't say I love it haha) however it didn't come with any...
Replies
9
Views
3K
Hi Everyone, I'm New to this forum and am hoping to obtain some advise if possible please? I have a situation where a megaflow system is...
Replies
12
Views
5K
A few weeks ago I posted this in another thread...: The tripping kept occurring, so I went back and moved a likely candidate circuit to the...
Replies
2
Views
1K
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock