Have noticed the fans that don't need the 3A fuse are at the top end of the price range,like the ventaxia inline fan and the Greenwood 100m wall fan(£80).
But can make the install easier.
Regards,S
Regards,S
I don't actually know but that is the purpose of the 3A fuse. I found a university study into this a while ago, can't find it now which found it to be highly unpredictable dependent on fan and/or fuse manufacturer.
I think most of the motors in domestic fans nowadays are covered as 'impedance protected' (ZP) as per UL 1004-2 requirements where they're less than 100 watts and their internal impedance is sufficient to prevent their temperature increasing above a certain point under a prolonged locked rotor condition. If so it's unlikely they'll have a thermal fuse on the windings.
A 3Amp fuse on the supply would only blow if there was complete winding insulation breakdown and a flash fault. I guess the thinking is that the internal wiring might be too small CSA to achieve a high enough fault current to achieve disconnection by the OCPD on the final circuit in the consumer unit.
Reply to Finally some common sense from a fan manufacturer? in the UK Electrical Forum area at ElectriciansForums.net
Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical
forum online. General electrical questions and answers can be found in the electrical forum.