Guys,

There are very few flats in this area and I have never done a new build on a block of flats, hence possibly a silly question!

About to get a contract to wire 8 new build flats above a chemist and night club.

Does the DNO put the meters and supply in to each flat or is this a cost my customer will have to incur?

Put this in the pub as a bit embarrased to ask in open forum!

THANKYOU,

JAmes
 
DNO requirements do vary from different regions.

However, SSE require meters in EACH flat.

To achieve this, you will need to install ducting, normally from the intake which will be on the ground floor somewhere.

They will then install a submain from the intake position to the flat and connect a local cutout and meter.

All you need do then, is install your CU in each flat as per the norm.

This a costly exercise and normally the client will pay direct.

Contact your DNO and they will give you a quote and all the info you will need.
 
Most flats i have seen have the meters in a communal ground floor cupboard from which you have to fit an isolator and run a sub main to each flat.

Again this could vary between regions.
 