FP200 3 phase rating?
T
Teddy Lop
Writing up a sizable EICR, one circuit is utilizing FP200 type cable (don't know the exact brand sorry I know they differ) for a 3 phase condenser, but the only ratings I can find for any softskin cables state single phase AC.
Is 3ph AC even permissable?
What you need to look at is the voltage rating of the cable and at a minimum it is likely to be 300/500v so this is fine. If the cores are contained within one cable this is also fine. If the cable is exposed to sunlight this probably isn't fine.
Sorry should have been clearer but I'm looking for a current carrying capacity; the tables I've observed all state DC or 1P AC
Use Table 4D2A.
Oh, I was under the impression fp had different ratings, think I was confusing it with that "refer to manufacturer" SY stuff, thanks
All I need now is zs for MG 60947-2s, which you think would be easily accessible info wouldn't you
Includes Zs for MG 60947s
Unfortunately it's £10.
All of the information for MG stuff is freely available from Schneider
