What cert do you now issue for a board change? I always have done an installation for the board , then a periodic for the circuits, but with periodics being replaced with eicr I assumed that it was now an installation and an eicr? Am I doing too much?

In a word yes.
you use an EIC for your CU change but the schedule of test results is pretty much the same for an EIC and a EICR , so just one cert will suffice.

Unless of course the customer is paying for a EICR as well as the CU change , in which case issuing seperate certs is perfectly fine.
 
Last edited by a moderator:
What cert do you now issue for a board change? I always have done an installation for the board , then a periodic for the circuits, but with periodics being replaced with eicr I assumed that it was now an installation and an eicr? Am I doing too much?
EIC for a CU change
 
To be honest the odds of someone being killed by a belt from an RCD protected circuit are slim to none in my opinion. I've had dozens of belts in my time on all types of circuit, and none of them have been particulalry bad.
 
So what youre saying is one outlet of a double socket had no earth connection ?
Well thats a fault with the socket isnt it ? it wouldnt show up on any sort of cable tests ???
dont really understand your point.

exactly my point is that wouldn't show up on any cable tests thats why relying on end to end tests etc.. wouldn't have shown up this fault. The proper procedure of cross connecting line and earth then testing at EVERY point including BOTH outlets of of a double socket would have revealed the fault. what's not to understand?
 
exactly my point is that wouldn't show up on any cable tests thats why relying on end to end tests etc.. wouldn't have shown up this fault. The proper procedure of cross connecting line and earth then testing at EVERY point including BOTH outlets of of a double socket would have revealed the fault. what's not to understand?

Both outlets has never been part of the procedure. Its a wiring test as biff says.
 
I agree with Guitarist here,
A full set of tests done on a CU change, as I have had polarity reversals Show up during testing (Full RFC tests) at either a 'DIY spur' or in case on one S/O on the ring (DIY replacement ?), slack Neutrals in the S/O but twisted together so it doesn't show on an end to end, the list goes on.

Besides on a CU change, you are signing to say any circuits you re-instate are safe to do so.
 
exactly my point is that wouldn't show up on any cable tests thats why relying on end to end tests etc.. wouldn't have shown up this fault. The proper procedure of cross connecting line and earth then testing at EVERY point including BOTH outlets of of a double socket would have revealed the fault. what's not to understand?

Thats a good point and i cant disagree with your method.
But the purpose of the 3 step ring continuity test is to confirm connections of the wiring , not to check if accessories are faulty.
A earth loop test at each outlet would have discovered the duff socket without doing the cross connecting.
 
Both outlets has never been part of the procedure. Its a wiring test as biff says.

agreed, and it has never really been part of my procedure until recently, and low and behold.... look what I found! How common is it? rare probably. But it does happen, as I have proven. The regs class a double socket outlet as two outlets, so really, and from now on I will, class, and test them as...TWO outlets.

I'm only here to glean from others, and share what i have learned in the field. I have no axe to grind. Let everything be on your own conscience.

Peace.
 
Thats a good point and i cant disagree with your method.
But the purpose of the 3 step ring continuity test is to confirm connections of the wiring , not to check if accessories are faulty.
A earth loop test at each outlet would have discovered the duff socket without doing the cross connecting.

That is his point, by doing the 3 step test and checking at each S/O would have shown up the fault during dead testing, and presumably corrected before any live testing commenced
 
Thats a good point and i cant disagree with your method.
But the purpose of the 3 step ring continuity test is to confirm connections of the wiring , not to check if accessories are faulty.
A earth loop test at each outlet would have discovered the duff socket without doing the cross connecting.

Can't disagree Biff, but speaking for myself and many others surly, when required to provide a Zs from a RFC, who tests at EVERY outlet? I didn't used to. Did this time and found this and now forever will.

Peace
 
That is his point, by doing the 3 step test and checking at each S/O would have shown up the fault during dead testing, and presumably corrected before any live testing commenced

Hmm , thats debatable as thats not the purpose of the ring continuity test.
And as the fault existed anyway while the installation was energised , discovering the faulty socket during live tests is hardly a major threat / risk / inconvienience.
But im off to bed now lol.
 
Hmm , thats debatable as thats not the purpose of the ring continuity test.
And as the fault existed anyway while the installation was energised , discovering the faulty socket during live tests is hardly a major threat / risk / inconvienience.
But im off to bed now lol.

Not having a go at anyone Biff, each to their own, and if they are happy signing stuff off untested then that is up to them.

There was a thread on here not so long ago about a plumber who was killed due to a miswired socket (polarity), and the sparks involved ended up in court, I would rather do the tests properly and sleep easy that's all.

I would just like to point out the testing and minor fault fixing should be factored in to a CU change price anyway, majors are a different matter and should really be picked up at the initial survey/quick test stage.

As I say each to their own.
 
Hi mate is this job AT MY BRUVS as i am finding similar probs to you
my tutor at college asked me why i tested at both sides of doubles i said because they are both outlets and also value can be significantly higher as i have found
continuity on lighting some switches were giving readings with it switches off

started of at somewhere in the region of well over 4 ohms the meter wouldnt give a constant reading it was as high as 6 some of the time
LOW IR
shower 6mm OK at 45A dp switch feeding 230v fan zone 1 1.0mm / also feeding a FCU for Old C/Heating supply
spurs of spurs
mutiple connection blocks no tape loose connections
hidden JBs with loose connections
rodent damage hidden under a board were i was looking for a hidden JB for landing and loft light were it was giving a high continuity reading
bonding to water after branchwork High readings before and other side
Ip ratings not met on newer single rcd board
circuits still connected in old wylex 4 way going nowhere and about 4 circuits in each
downlights in kitchen 2 supplies switches at side of each other 2.5mm feeding 1.0mm again chockblocks
twiisted Ns not in terminals at sockets
twisted cpcs not in terminal at socket
metal back boxes protruding from wall
grommets missing
no sleeving on earths
switch wires not identified
sockets are suspect to say the least think ring is in JBs most sockets downstairs have 1 cable so spur of JB no prob if not ideal
then spurs of spurs
some sockets had ok reading at one outlet of double socket and at other as much as 2-3ohms
some wouldnt switch off
step 2 and 3 readings are nowhere near within 0.05ohms of each other
cracked sockets and switches with heat damage
every time i found a fault i would repeat the test and slowly but surely reduce the continuity readings to a more acceptable reading and increase the IR


mate i could go on so now like you I test evrything borrowed neutrals even between the disconnected NOW DEAD circuits and the remaining circuits to see if there is continuity still and IR between them


and have condemned the lights and told him unless he lets me under floorboards to have a look its staying locked off as i still have a L-N 0.14 to 0.27 Meg and yes evrything is unplugged disconnected removed linked out
this wouldnt show up if i just tested with L&N joined to earth then i got a reading of 80+M/ohms

I suspect the lighting problem stems from the 10K kitchen he had done
its not worth 1K
best bit granite worktops the rest any muppet could chuck together
they just slung cables behind cupboards and even behind fridge High level double with cables jsut dangling down and disappearing behind cupboards he could of at least used cable clips for 10k

the transformer for pelmet selv lighting is sitting on top of the freezer with untaped chock blocks for the connection point sitting along side the transformer

anyway woooden floors newly laid carpets coming up upstairs and if its bad i will give him the good news lets rewire the lights and sockets LOL and get some chases in the plastering he had done other year lol
 
Last edited:
Have any of you seen the elecsa newsletter SPARK
fatality prompts warning to installer community after the death of a young mother
and are urging electricians to follow correct procedures after unearthing a catologue of failings
in a new block of flats in west bromwich
and cutting corners when testing as the guy ended up in the dock before the man
 
Have any of you seen the elecsa newsletter SPARK
fatality prompts warning to installer community after the death of a young mother
and are urging electricians to follow correct procedures after unearthing a catologue of failings
in a new block of flats in west bromwich
and cutting corners when testing as the guy ended up in the dock before the man

Not yet, it is in the pile of junk mail I get lol.
 
I'm glad that you feel knowledgeable and experienced enough to "know better" than the rest of us :)

Look pal, if you get some kind of peverse saitisfaction out of treating every job you ever do as a rerun of your college testing and inspection assessment then thats cool, I got no problem with that, but Im too busy trying to keep all my clients happy and earn a decent living, to be spending hours of my life trying to satisfy irrational urges that I dont actually have. I have ample confidence in my own judgement.
 
LOL
basically they are saying he was cutting cormers so issuing fake EICs which is fraud and negligence as well as idiotic and dangerous etc
a test sheet was signed off without proper checks being completed one was the insulation resistance test is often done sometime before the installation is completed and the system as whole tested to get power for trades and should be done again once everything is complete he was just saying it had been done
the eic is what they will use to find and incriminate you if anything is wrong with the system

she had a leak and was mopping up leaking water from a faulty heater it doesnt go into much detail but think they are after taking action against the person who signed etc

it wasnt jsut her flat it was the whole block of flats that had issues
 
Look pal, if you get some kind of peverse saitisfaction out of treating every job you ever do as a rerun of your college testing and inspection assessment then thats cool, I got no problem with that, but Im too busy trying to keep all my clients happy and earn a decent living, to be spending hours of my life trying to satisfy irrational urges that I dont actually have. I have ample confidence in my own judgement.

It is not that Dave,
I was T&I ing long before I got my 2391 or registered, but when you have been testing for any length of time, and come across some of the naughty faults that I, and probably others on here have, you learn to test properly, and more important the reasons why.
Even more so, when my name is on the documents.

Iam not meaning to come across holier than thou, but some of the downright dangerous stuff I have come across just reinforces all the more the reason to do it, some things make me shudder to think what could have happened.
It can be all to easy to miss things, and at best you will get a call back, at worst... in the dock.
I don't want anything to ruin my reputation that's all.
 

Reply to Full spread of tests after CU change. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
621
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
599
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
715
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
829

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock