Doing an EICR in a commercial building, taking on the advice from last post I was doing the IR individually rather than across the entire board, circuits wired in singles so had to locate the correct neutrals when I found this on 2 circuits, wondered if anyone had come across this before:

With Neutral disconnected I measure 400v between N & L1/L2, 0v between N & L3 so I presume its a L3 conductor, I also measure 230v between N & E

Reconnect the neutral and I measure 230v between L1/L2/L3

Need to look further into it but any thoughts appreciated
 
Maybe that neutral is borrowed somewhere along the final circuit to provide a return for another final circuit.
 
You may be right, its such a simple lighting circuit I'd be surprised but who knows who last worked on it, I made a typo its actually 3 out of 5 circuits like it.

The fluorescent lights are plugged into a galvonised track, there are 3 switches and 5 tracks.
 
Hang on, I just re-read you first post. Did you disconnect the neutral on a 3-phase final circuit that was still live? If you did it would have assumed a potential approaching that of the phase with the highest load which fits the test results you gave.
 
its a 3p board but the lighting is obviously single phase, switched off the mcb and measured 230v between N-L1/L2, switched the mcb on and measured 400v N-L1/L2 which made me think it was a phase conductor as I measured 0v between N-L3

It was definitely the correct neutral as the lights didn't switch on without it
 
The results you are getting correct once you disconnect the neutral from the neutral terminal its at the same potential as L3!
What are you expecting between N and L3 then!
 
The results you are getting correct once you disconnect the neutral from the neutral terminal its at the same potential as L3!
What are you expecting between N and L3 then!

Then why on only 3 out of 5 circuits did I measure this?

I wasnt expecting 400v between N & L1/L2 and 230v between N-E

Thinking about it could it be the live returning through the emergency fittings..... hence the 400v N-P and N-E
 
Have a think about it the Neutral is on the L3 circuit so you disconnect the N and if the cct is energised it is the same potential as L3 so N E 230 volts
N L1 /L2 400 or am I missing the obvious here?
 
Perhaps its me missing the obvious??

With 1L3 switched off and the N disconnected I measure 230v N-L1/L2 and 0v N-E, energise 1L3 and I get 400v N-L1/L2 and 230v N-E which must be the return path from the emergency fittings hence only on 3/5 circuits.....
 
I would be IR testing the circuit you might find a Neutral to Earth fault on that circuit IMO !
 
Perhaps its me missing the obvious??

With 1L3 switched off and the N disconnected I measure 230v N-L1/L2 and 0v N-E, energise 1L3 and I get 400v N-L1/L2 and 230v N-E which must be the return path from the emergency fittings hence only on 3/5 circuits.....

You just answered your own question again, with 1l3 OFF N -E 0 V
When energised N-E 230V! Because the neutral is now live!
What are you trying to prove by even doing this? It's not even a test you should be doing!
 
You just answered your own question again, with 1l3 OFF N -E 0 V
When energised N-E 230V! Because the neutral is now live!
What are you trying to prove by even doing this? It's not even a test you should be doing!

Tested it because I had a strange reading??? if 230v to e was normal it would be on all circuits not just a select few
 