Discuss Fused spur dilemma in the UK Electrical Forum area at ElectriciansForums.net
Hello, need to run a supply to a tyre air line at a petrol station. No info on it but think its probably around a kilowatt, definitely not over 3kw.
Should probably be on its own dedicated circuit, but going to cost more.
There is a socket inside that I could spur off and save alot of extra work and materials
Is it really just good practice to keep outdoor equipment on a separate circuit rather than spurring of a ring? Prevents nuisance tripping.
Can't see anything in regs that says it's not possible to connect this type of equipment to the ring as long as it is under 3kw.
Just wanting to no what others think on situation, appreciate any replys.
If the supply is to the compressor you may be asking for trouble . Sometimes the cost is not always , but may include financial.
Yes I'm aware there is special regs when it comes to petrol forecourts that's why I don't do them.
Didn't think the airline would be a problem as long as it's located well away from pumps, which it is.
The circuit that I would be spurring of is serving the office and is on a TT installation as preferred for petrol stations. Just wanted to know was there any other limitations on spurs other than 3kw load and voltage drop.
Hello, decided to put the compressor on a separate circuit.
Able to keep cost down by using the car wash supply that is no longer in use.
Will test to make sure cable is ok.
Had thought compressor should be on its own dedicated circuit, owner pushing to take off socket to keep cost down.
Apart from it might cause fault 5 or 10years down the line and trip out sockets inside couldn't really think of any other reason why it couldn't be done. It was on a TT earthing system so no issue with tncs outdoors.
So really in this situation although not ideal you probably could connect the compressor and still comply with regs?
Or is it best to keep spurs inside regardless of earthing system?
Also just thought would it be possible the compressor motor could cause a spike in ring circuit and effect I.T equipment? Computers on that circuit,
Or would that size motor have little effect on equipment in other parts of circuit. Maybe over thinking it now.
Appreciate any replys, thanks
Bas
Do you need a spur or spurs.
Don't need any spur now, going to use cable that was used for car wash.
Just got me thinking what reasons there are for not connecting this type of load to a ring circuit.
Its under 3kw, voltage drop wouldn't have been an issue, so I think it would have meet the regs, yet most electricians would probably not be happy with this.
Think it's mainly down to good practice what do yas think?
Supposing every thing else is ok in another situation other than a filling station , depending on the size of your compressor you would have to consider the motor inrush . 3kw? +whatever else is on the RCD protected circuit.
Ok think I'm right in saying there's no set rules as to what can and can't be connected to a ring circuit, as long as loading is taken into consideration, and any other requirements for regs are met.
Basically you could get away with the compressor on a spur there's nothing to say otherwise.
Reply to Fused spur dilemma in the UK Electrical Forum area at ElectriciansForums.net
  • Locked
5K
Current setup: there is 4mm Double Insulated armoured cable running from the kitchen to shed's location. In the kitchen this cable is connected to...
Hi all, Looking for some advice if possible please! Got one if then jobs that you get roped in to and that’s turned from a quick simple...
Hi, Just been and looked at a job done recently by a colleague. SWA dedicated 16A supply from a garage consumer unit to a external socket outlet...
Hi Guys, This is a bit of a long post, as I'd like to detail everything, and take input from others. Let me start by saying that I did my...