Could you expand on that a little GayOwl?
I think you're referring to 134.1.1?
If you are then I can see the difference in the wording of the reg compared to the BGB, however..
"The Installation of electrical equipment shall take account of the manufacturers instructions"
Does that still mean we HAVE to follow MI's as in the previous 134.1.1 or does it mean we can now give it 'consideration', and if we deem the install to meet all other regs and to be safe we do not have to follow MI's?
I think Richard summed it up nicely. I interpret it as giving it consideration as you say. I had a issue with some MI's a while back. Can't recall the full details but it was an oven and related to the cable they stipulated should be used; I think they said T&E should be used or they said 6mm cable should be used on a 2kW oven! I opted for a HOR type cable to connect the oven instead if I recall correctly. I noted this as a departure on the cert. I suspect we are meant to still note such departures, but we are not now considered to be breaking the regs by doing so.
Neil
Hi Lee,
The text on that Silavent gumph does say 'suitably fused' mate! Personally I rarely use a FCU on them...triple pole isolator yes.
It says suitably fused, in accordance with IEE regulations though. I would take this as the CCC of the cable connecting the fan should be sized according to the OCPD. No where in the regs does it say a fan must be fused to 3amps.
Fair play. Just noticed it and couldn't resist! :smile5:
Totally agree with the above posts. Only local isolation needs to be provided for a fan (when fed from the lighting circuit on a 6-10A MCB in 1.0-1.5mm). The 3A bit from the manufacturers is just covering their backsides.
I have never provided a 3A fuse for any fan I have ever fitted and never will regardless of instructions. As Richard says, a lot of instructions need to be viewed and digested with a large pinch of salt. A huge proportion of MIs are mere buttock covering documents, often provided for a range of appliances/equipment and not relevant to the model in your hand. Use your nowse and distil the wheat from the chaff.... this applies to all guidance offered in written or verbal form !
Neil
I think that was a good idea to note it on the cert as it shows you have given it consideration. Although, I suppose it's not actually a departure from the regs as the regs state 'take into account', you have taken them into account and made an informed choice to use HOR cable (which lots of other MI state to use!). So really you have still followed the regs!
This was pre AMD3 mate, so technically I still should have blindly followed the MIs!
ive probably fitted close to 1500 fans of various brands, greenwood, vortice, vent axia etc and have never fused them down. These are all of course on new build homes and wired via 3 pole isolator. Never had an issue and sleep fine at night. Just dont over think it.
I've not read all the way back but if it says it in the manufacturer's instructions why wouldn't you fuse it down? I fuse all fans down and code un fused fans as a code 2 on an eicr.
Sent from my GT-I9505 using Tapatalk 4
Do you work for BG? Lol