Yep, assuming you have a spare way, you’d also want to correct configuration ie selectively of rcds/rcbos etc.....what sort of loading are you planning in the outhouse?.....any extraneous parts etc? If using the additional protection at the house consumer you’ll need to make sure the new total loading doesn’t exceed the rcd max....
 
As above!

If it is not critical (i.e. just lights and occasional 13A socket use) so you can live with poor selectivity then feeding it from a MCB in your CU is OK. Ideally you don't want it on any home RCD circuits due to the additional inconvenience and time locate any fault out there, and most "garage CU" come with a 30mA RCD and a couple of MCBs anyway.

If you have plans for a workshop, hot tub, etc, then you would be better splitting your tails and feeding it from a fused switch. Push the upstream fuse as high as your cable end's Zs will allow for meeting 5s disconnection, and try to keep the downstream MCBs to around half of that if you need good selectivity. The downstream MCBs can provide the overload protection for the SWA cable.

If you really worry about big faults, try to keep your fused-switch below around 60% of the DNO fuse rating!

Look at your load/use-case and start juggling the numbers...
 
Last edited:
Just to add to the above, adding a small consumer unit to your garage falls under Part P and you will need to notify your local authority. This will cost money.
 

Reply to Garage consumer unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I wondered if it is OK to have 2 x Main Switches in the same consumer unit. One feeding the RCBOs in the House and one feeding the CU in a garage...
Replies
16
Views
772
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi. Can a horizontal 200A consumer unit be fitted vertically, or is there a vertical configuration? I have a 350mm wide space...thanks.
Replies
19
Views
817
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
742

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock