I am going to replace a garage consumer unit. The existing feed from the main CU in the house is via 2.5mm armoured cable and is on a 16A MCB with 80A RCD. The new unit is supplied with a 40A RCD, 32A MCB & 6A MCB. The cable method is "A" so 20A max. I will swap the 32A MCB for a 16A for the sockets but my question is can I use the 40A RCD??
 
yes . because the 40A rating of that RCD is the max. current it will withstand. nothing to do with overload.
 
i would uprate the 16A MCB at the main CU to 20A though.
 