W

william7900

Hi friends,

I have been reading threads concerning garage earthing arrangements. Advice was given to extend the earth from the house to the garage. Please may I comment that this is a dangerous practice because if by accident someone went through the SWA cable with the mower etc, the result would be catastrophic, due to the fact that in the garden you will be in contact with the earth and a perfect conductor for electricity and receive a severe shock. The earthing system for a garage should always be TT, using earth rods and trying to achieve a resistance of 200 ohms. You may have to use more that 1 earth rod to acheive this. The garage unit should always be RCD protected.

This is why on building sites all the equipment is supplied by transformers which gives a separated environment and no earth is used for safety. Hope this helps.

Regards,

Bill
 
i fail to see why the type of earthing at the garage would have an effect here. either way, you are in contact with the earth when you cut the cable. the cable is earthed at the supply end anyway, no matter what earthing system you have at the garage.
 
Hi friends,

I have been reading threads concerning garage earthing arrangements. Advice was given to extend the earth from the house to the garage. Please may I comment that this is a dangerous practice because if by accident someone went through the SWA cable with the mower etc, the result would be catastrophic, due to the fact that in the garden you will be in contact with the earth and a perfect conductor for electricity and receive a severe shock. The earthing system for a garage should always be TT, using earth rods and trying to achieve a resistance of 200 ohms. You may have to use more that 1 earth rod to acheive this. The garage unit should always be RCD protected.

This is why on building sites all the equipment is supplied by transformers which gives a separated environment and no earth is used for safety. Hope this helps.

Regards,

Bill

You need to read this thread... http://www.electriciansforums.net/e...159-good-guide-exported-pme-outbuildings.html
 
Hi friends,

I have been reading threads concerning garage earthing arrangements. Advice was given to extend the earth from the house to the garage. Please may I comment that this is a dangerous practice because if by accident someone went through the SWA cable with the mower etc, the result would be catastrophic, due to the fact that in the garden you will be in contact with the earth and a perfect conductor for electricity and receive a severe shock. The earthing system for a garage should always be TT, using earth rods and trying to achieve a resistance of 200 ohms. You may have to use more that 1 earth rod to acheive this. The garage unit should always be RCD protected.

This is why on building sites all the equipment is supplied by transformers which gives a separated environment and no earth is used for safety. Hope this helps.

Regards,

Bill


You are talking rubish. What if someone is using and extension lead from their house and cut it with their mower? Surley the earth from the house is at the mower and they are standing on the earth. So it has moved on fom not exporting a PME earth to not exporting any earth.
 
Last edited:
I fear for the future of mankind!

The trouble is Tony, all this scaremongery about PME, has been going on for a very long time now, and it's convinced an awful lot of electricians in the process.

The old Leccy boards spent years ridding 100s of 1000s of homes of TT systems by providing a fully functional PME earthing system to these old installations. Now we have plonkers trying there best to reinstate or creating new TT systems!! I can only put this down to ignorance of the real facts, in preference to all the old wife tales that are being banded about to this very day!!!! The OP of this thread being a perfect example...
 
E54 we’re from the same era and both singing from the same hymn sheet.

I’ll stick to my statement that exporting earths is beneficial.
Both you and I have installed earth nests.
For my part they have included steel framed building covering hectares. All linked together. I’ve run dozens of radial sub feeders and not one with a supplementary CPC. Why because they were earthed through the structure of the building! I would have received a sever battering around the head for suggesting running a 95 CPC along side a 185 SWA.

Just as an aside the last nest I had anything to do with testing the commissioning engineer came out with the statement “I don’t know why we bothered” as he looked up at 10,000 tons of steel. As a matter of course I’d bonded the incoming services. 3 X 8” steel water mains will beat anything you can knock in the ground.
 
E54 we’re from the same era and both singing from the same hymn sheet.

I’ll stick to my statement that exporting earths is beneficial.
Both you and I have installed earth nests.
For my part they have included steel framed building covering hectares. All linked together. I’ve run dozens of radial sub feeders and not one with a supplementary CPC. Why because they were earthed through the structure of the building! I would have received a sever battering around the head for suggesting running a 95 CPC along side a 185 SWA.

Just as an aside the last nest I had anything to do with testing the commissioning engineer came out with the statement “I don’t know why we bothered” as he looked up at 10,000 tons of steel. As a matter of course I’d bonded the incoming services. 3 X 8” steel water mains will beat anything you can knock in the ground.
Well BS7671 states that the metalic structure of a building CAN be used as a reliable means of earthing doesn`t it...
542.2.1 (p 127) states:
1...earth rods or pipes
2...earth tapes or wires
3...earth plates
4...underground structural metalwork embedded in foundations
5...welded metal reinforcement of concrete (exept pre-stressed concrete) embedded in the earth
6...lead sheaths and other metal coverings of cables, where not precluded by regulation 542.2.5
7...other suitable underground metalwork
 
Hi friends,

I have been reading threads concerning garage earthing arrangements. Advice was given to extend the earth from the house to the garage. Please may I comment that this is a dangerous practice because if by accident someone went through the SWA cable with the mower etc, the result would be catastrophic, due to the fact that in the garden you will be in contact with the earth and a perfect conductor for electricity and receive a severe shock. The earthing system for a garage should always be TT, using earth rods and trying to achieve a resistance of 200 ohms. You may have to use more that 1 earth rod to acheive this. The garage unit should always be RCD protected.

This is why on building sites all the equipment is supplied by transformers which gives a separated environment and no earth is used for safety. Hope this helps.

Regards,

Bill


A wind up methinks.
 
Hello guys,

You must understand that for TNCS systems the earth and neutral are the same conductors. Now if the neutral were disconnected due to a supply fault, the live conductor will now look for another path to complete the circuit which will be the bonded conductors on your gas and water pipes. Now just suppose at the same time you were digging your garden with your kango and made contact with the earth that you had run to your garage, you will form another low resistance path to earth and receive a severe shock. This is why electrical suppliers forbid the exporting of the PME earth.

Now for TNS systems you won't get this problem as the neutral and and earth conductors are separate. However the bonding to the garage from your house must be at least 10mm. For most installations this means running 2 cables as most garages use 4 - 6mm conductors. So again I would use a TT system because it is expensive to run a feed to the garage in 10mm swa unless it is a short run.

Hope this clears up the confusion.

Regards,

Bill
 
No it doesn't, as it is you that is confused.
You don't need a cable in the garden for a loss of supplier's neutral to be a problem.
Any exposed or extraneous-conductive-part connected to the earthing will become live.
Your washing machine, your central heating even your crittle windows (if they're bonded).
This is one of the reasons, why in most other countries an earth electrode is installed at the origin of each installation.
However the loss of the supplier's neutral is not something that is seen as a problem in the UK, as there are measures in place to guard against this.
As for the cable in the ground, it should be at a depth so as to not be damaged when digging the garden.
 
It's unreal that there are these people, still around out there!! These people will happily go around making TT systems willy nilly, probably using those 3/8'' 1.2 m excuse of ground rods, that can very easily leave an installation void of any earthing during adverse weather/temperature conditions. Because they know no different, they will ditch a superior earthing system and will spurt out this total nonsense about ''it is forbidden'' to export PME!! who the hell told you that?? Well....how about ''Extending the equipotential zone then?? I take it, you then think that an outside socket outlet on a PME system is also banned??


William, the only confusion in what you have posted is yours, as you obviously have no idea what your saying here. You have been wrong in just about everything you have posted on this subject. Please go and read the Sticky on this subject, then come back here and try and tell us that were all wrong and that your right!!
 
Guys,

The suppliers do not reccommend it as a matter of safety. This is why we have regulations to protect us in that 1 in a million chance of being injured. Unfortunately not all of us wish to adhere to them until it affects us. Just as a matter of interest the part P of the building regulations came about due an MPs daughter being injured by an electrical fault.

Keep safe guys.

Regards,

Bill
 
Bill that last reply is vague and unhelpful to your pointless arguement. Firstly you said the DNO does not allowed us to export a PME earth now you say they don't recommend it. Which is it? Which reg are you talking about. There have been a few others that have said about regs but could not find this hidden reg to back up their argument. You are wrong plain and simple. Just give up with argument.
 
Take a look at this Bill.
http://electrical.------.org/wiring-matters/16/elect-inst-outdoors.cfm?type=pdf


Sorry for the repetition - Just spotted someone further back has already pointed this document out.
 
Last edited by a moderator:
Guys,

Just as a matter of interest the part P of the building regulations came about due an MPs daughter being injured by an electrical fault.

Keep safe guys.

Regards,

Bill
She wasn't injured, she was killed. However, her death came a long time after the consultation process began which resulted in Part P. Merely a tragic coincidence.
 
Guys,

The suppliers do not reccommend it as a matter of safety. This is why we have regulations to protect us in that 1 in a million chance of being injured. Unfortunately not all of us wish to adhere to them until it affects us. Just as a matter of interest the part P of the building regulations came about due an MPs daughter being injured by an electrical fault.

Keep safe guys.

Regards,

Bill


Stop, and think about what your saying. Based on your electrical knowledge on how earthing/bonding systems work you will come to the same conclusion as the vast majority here. Your basing your reasoning at the moment, on myths and scaremongery that originated from those that opposed the introduction of PME in any form for general distribution.

As i stated in earlier posts, you have been wrong in just about everything you have posted on this subject to date. You are also very wrong in the ''one in a million'' statement, the chances of experiencing let alone being injured, is far far greater than that!!

The only restrictions to the use of a PME system are well founded, but do NOT include extending such a system to a domestic outbuilding, shed, or garage!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Garage Earthing system
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
25
Unsolved
--

Advert

Thread statistics

Created
william7900,
Last reply from
Engineer54,
Replies
25
Views
6,210

Advert

Back
Top