holte end74

if i supply a garage cu with SWA does the cable need to be RCD protected is it ok to come off a rewireable cu .
 
Preferable to have a circuit breaker but BS3036 should be OK if calculations are correctly done.
If it is a TN earthing system then SWA does not need RCD protection as it has an earthed metallic sheath (so long as you earth the armour!)
 