I looked at a job today to add a new shower circuit. The c.u is close to the gas meter, less than the 150mm recommended. It is not going to be possible to move it as the customer won't pay the cost. Seeing as im altering an existing circuit not changing the c.u does anyone know if I have to put in a barrier or not? If so any ideas what to use?

Many thanks
 
Have rang gas safe before, on the basis from the gas meters view, and its down as ncs. Or to rectify this, adequet electrical insulation placed inbetween the two would be ok. If it posses no risk of danger, it should be ok.
 
I looked at a job today to add a new shower circuit. The c.u is close to the gas meter, less than the 150mm recommended. It is not going to be possible to move it as the customer won't pay the cost. Seeing as im altering an existing circuit not changing the c.u does anyone know if I have to put in a barrier or not? If so any ideas what to use?

Many thanks


"Hello smu_diddly,

From a Gas Engineers point of view the Gas Safety Regulations / Installation practices pertaining to this distance between the Consumer Unit and a Gas Meter / Gas Meter Regulator [`Governor`] are regarding a possible Fire at the Consumer Unit.

Obviously a Fire at the Consumer Unit could still affect the adjacent Gas Meter in many situations whether it was 150mm away from the Gas Meter or any other distance - especially in an understair cupboard or other enclosed area / cupboard - but that is the minimum requirement / distance without a partition.

Although it is stated that a partition must be both ` Non Combustible` AND `Electrically Insulated` - So there is obviously an Electrical reason also - I have never seen this Electrical requirement explained / defined in any written form.

Regards,


Chris - Heating Engineer and Gas Safe Registered Gas Engineer
 
Fix a sheet of paxoline cut to size, corner braces bolted thru sheet and screw and plugged to the wall. Just add the cost to you bill to cover costs (eg. £20 nominal charge).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
gas meter location
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
smu_diddly,
Last reply from
smu_diddly,
Replies
6
Views
1,486

Advert

Back
Top