where is the big boys,need help pls can i bond Gas & Water with the one run 10mm earth cable.
tncs system ,,, the reason i ask is both at one corner,i normaly run one for the Gas & one for water ,
 
i.e. continuous and looped at the first point, not relying on the clamp for continuity as wet-pants will be bound to fiick it up.
 
nowt more to add...

apart from dont attempt to piggyback (cable tie) the 10mm G/Y to pipework on its run....its a non-conformance..
 
Wrong. There is NO REG saying it has to be continuous. The GN suggests continuous as best practice.

Hmm, I was taught you shouldn't have a join at a clamp, it had to be continuous but perhaps it is only best practice guidance. I've also seen cables joined with a crimp connector (not at the clamp), don't know if that fits with best practice or not?
 
Hmm, I was taught you shouldn't have a join at a clamp, it had to be continuous but perhaps it is only best practice guidance. I've also seen cables joined with a crimp connector (not at the clamp), don't know if that fits with best practice or not?
nowt wrong with crimping...if its done rite...
 
To be honest I have always thought it was regulation so I have possibly issued a couple of incorrect C3s in my time, I'll admit my mistakes though.
 
are you sure you cant cable tie to cold water pipes ? whats the worst thing that could happen ..... you could earth the pipe if it was cut
 
To be honest I have always thought it was regulation so I have possibly issued a couple of incorrect C3s in my time, I'll admit my mistakes though.

There is not a reg saying you have to do it but the arguement is that it goes against reg 528.3.3 --- i.e. someone changes/removes the pipework and not being continous you potentially loose the bond to everything!

Giving a C3 seems a fair assessment in that it could be improved to meet 528.
 