I'll raise the issue of the load bank with the customer, as the use it has now is well under its capacity.
I'll speak to the Alarm guys and discourage the auto start, I have installed a couple of sockets near the inverter so that the battrey chargers can be used, when the gennie is on for other reasons.
Any recommendations on type and size of loab bank?
The auto start is fine for powering up the overall installation from the gate, but definitely not for the sole purpose of charging alarm batteries!! lol!!
Whatever your normal running load might be, then add an appropriate KW number to bring the Gen-Set's running load to around 65 to 70% of it's rated capacity That will be the size of load bank required to sustain long service from your Genny... Virtually all load banks are resistive, they can be brought on line in stages, preferred (also giving you a wider scope of normal running loads for the present and the future) or direct on line.
Take in to account the load bank is just wasting energy. Energy that has to be paid for in terms of fuel used.
So much for green energy using solar power for the alarm when next to it will be a load bank producing 30/40KW of waste heat.
The whole set up is ridiculous.
Hence the very reason for always specifying a gen-set to the load it is expected to supply, plus a realistic surplus, for any foreseeable future loading increase(s)....
In this instance, your spot on Tony, it is indeed a ridiculous set-up!! Mind they could always locate the load bank in the mess hut or whatever, to heat the place up for the lads!! lol!!!
Unfortunatley there was no conversation regarding Gen Set specification, as there was no know spec regarding the load, The Genny came out of a Bank which was being developed by the customer, he just had it shipped on site and said hook it up and put a few lights and sockets in the workshop, and when you joke about the mess hut, we put a few extra sockets and lights in there as well!!!
I know it's mad, but to say it's all arse about faced, going forward who knows what the customer will think of adding next.
Originally they had a little single phase portable petrol genny, which just about boiled the kettle, but that got pinched when the break in happened...
I know I’ve been a bit cruel but look at it as I did when I read you’re first post. I know the situation is not of you’re making. If the owner caries on with this gen set it’s not going to last five minutes before the engine is knackered, that added to the fuel costs, it’s going to end up costing a fortune.
I don’t envy you trying to get him to see sense.
Tony, Don't apologise, I agree with all your comments, yes it is a mad set up.
The Solar panels were not put in for green energy, they were there to power the alarm system before the genny came on to the scene, so I'm not losing sleep over that expense.
And as far as fuel is concerned, again I don't think the customer is worried too much either.
The Genny came as a freebie I believe from one of his developments as I mentioned earlier, If I can persuade him to extend the life of the set beyond the end of the year, then great.
One other question, would bringing a load bank on a rental term every couple of months or so, just to clear the wet stacking, would that be a viable option?
No, it needs a reasonable loading most of the time to keep the engine clear of deposits. A load bank just every so often will cause more trouble as you’re likely to get deposits flying around from the periods of light running. If it’s got a turbo, that’s not going to be happy either.
I had this problem about ten years back. We had a 1.5MVA set on emergency standby. To be honest I don’t know why we had it at all, it would just about keep the lights on. It was started once a week and run light, come the fateful day we needed it. It started OK, went on load and within 3 or 4 minutes the temperature went sky high and it shut it’s self down. Turbo and both cylinder heads knackered.
Thanks for the info Tony, have had a conversation with the customer regarding the Load Bank, and the auto start for the alarm guys, and he still wants to go with the auto start for their battery charger, and I have to research on pricing up a load bank....
So the saga continues...
Meanwhile going back to my original question, running two sources to the auto start on the genny should not be a problem should it?
Many thanks
If you've all ready got a remote start just parralel to that at the gen set.
Sounds like you've got a right divy there :bomb2:
You could be eco friendly and e-mail them. Hug a tree (it's dead though through carbon monoxide poisoning).
