im an electrician in Ireland and have recently found that when installing generator change over switches and using small kva generators (that tend to have a floating earth) the rcd within the fuse board does not work and the earth loop impedance is extremely high. my question is who's at fault? and how can we resolve this issue?
 
If you have a floating N, the earth loop will be almost non existent .
 
im an electrician in Ireland and have recently found that when installing generator change over switches and using small kva generators (that tend to have a floating earth) the rcd within the fuse board does not work and the earth loop impedance is extremely high. my question is who's at fault? and how can we resolve this issue?
It's because there is no longer any neutralising point in the installation.
 
Many generators can have a link added that joins N to earth at the output of the generator.
This will sort the earth loop out.
However manufacturers guidance should be sought first.
 