dawg25g

my customer is looking to install a generator at his caravan park to prevent overloading of his main incoming 150kva supply at his busy times. He intends to site the generator at the other end of the park to prevent the noise waking up the holidaymakers and he wants to use the existing circuits to be backfed from the generator whilst still keeping some of the park on the mains supply. Im thinking that if I install 4 changeovers at the incoming supply power house I can isolate the circuits from the mains that I want the generator to run but the problem is if some numpty started the generator without isolating the mains then there would be an almighty boom!!!!!. Could I fit a 200A contactor and another changeover at the generator position and the mains supply could hold it in the permanently open position? this would prevent power being fed back up the energised circuit? Once the powerhouse changeover was isolated then the generator contactor could energise and back feed the circuits that I want to power. Seems a bit messy and complicated but I really really don't want it to go bang! any suggestions please???
 
my customer is looking to install a generator at his caravan park to prevent overloading of his main incoming 150kva supply at his busy times. He intends to site the generator at the other end of the park to prevent the noise waking up the holidaymakers and he wants to use the existing circuits to be backfed from the generator whilst still keeping some of the park on the mains supply. Im thinking that if I install 4 changeovers at the incoming supply power house I can isolate the circuits from the mains that I want the generator to run but the problem is if some numpty started the generator without isolating the mains then there would be an almighty boom!!!!!. Could I fit a 200A contactor and another changeover at the generator position and the mains supply could hold it in the permanently open position? this would prevent power being fed back up the energised circuit? Once the powerhouse changeover was isolated then the generator contactor could energise and back feed the circuits that I want to power. Seems a bit messy and complicated but I really really don't want it to go bang! any suggestions please???

This whole post ispretty scary stuff but the underlined section really gave me the shivers. What if the contactor being held in the open position by the mains supply fails and returns to its normal position?

I'm not getting into this one and I'd suggest you commission a design from someone with experience in large generator installations.
 
To quote Victor M, “you can’t be serious”.

To supply part of a site via the DNO supply and part by the generator is a legal minefield.

Any danger of cross linking has to be “none existent”. This is possible, but only with interlocked switching.

If you want to go in to the method I’ll help by PM.
 
To quote Victor M, “you can’t be serious”.

To supply part of a site via the DNO supply and part by the generator is a legal minefield.

Any danger of cross linking has to be “none existent”. This is possible, but only with interlocked switching.

If you want to go in to the method I’ll help by PM.
I thought that was John M, Victor M was "I don't believe it" :D
 
Yep, Castel keys/ keyed interlocking would be a must with this type of setup. It's not particularly complex but there's certain rules must be followed and it's not the kind of system where there's scope for mistakes to be made whilst learning the rules the hard way. No offense to the OP but, at least in the design stage, my advice of seek the assistance of a professional with appropriate expertise still stands.
 
I can just imagine the response from the holidaymakers as the supply is changed over twice each evening.
The generator is going to have to run continuously to supply a section. A lightly loaded generator isn’t going to last long.
To what extent is this system overloaded?
 
might be a more economical solution to have a second supply installed by DNO. split the site across the 2 supplies. that cost would be offset by not having to buy a genny .
 
How big is the caravan site cause gens are noisy lol.
Telectix is on the money here, running the gen is going to cost a lot.
You could also avoid the boom by synchronizing the genny :D.
 
It's all been said already by Marvo & Tony me thinks!! lol!!

Far too many people have this idea about generators being the easy and cheap solution for a multitude of design deficiencies, when in fact they are anything but a cheap solution!! And that's even after any integration problems have been ironed out!!

Generators, especially prime power units are an expensive alternative to an equivalent DNO supply!! They will all require regular maintenance and servicing and fuel tanks having ample supplies. When you start doing the calculations on running costs, it tends to scare the living daylights out of most prospective owners, and the bigger the unit the bigger the costs!!!! ...lol!! And that's before you have seen the cost of purchasing any decent sized generator!!

Honestly, ...tell your park owner, to bite the bullet and have another DNO supply brought into the site!! lol!!
 
Going on the OP's record, we'll have to wait untill march 2014 for any answer.

Time to give up.
 