Tested one of our generators this morning, only about 76KW engine set. Started up fine, took the load of the building fine, connected a load bank, fine. Voltage readings all 240ish, temperature as expected, oil temperature as expected, coolant temperature as expected. 1.5hours later. Chug chug chug. Generator fails. Switches back to mains supply.
Fault on genny is “alternator volts fail”.
My first instinct is failed AVR. Runs genny again off load, readings are 240,241,242v (3phase obviously). So now what? Lol.
Possibly a faulty alternator? Is it worth checking the stator winding? I’m electrically biased and my mechanical knowledge is basic I’ll prewarn you. Thanks in advance.
 
Does the standby set have any bushes that may be worn down to far and not making contact on the alternator slip rings?
 
Like I have said hundreds of times here, the Jocks are constantly pi$$ed lol, say no more pmsl
 
‘Chug chug chug’ to me suggests that maybe the engine has an issue maybe fuel filter or the water separator hasn’t been emptied in a while.
Ah yes Dave, couldn't really be electrical, if the Prime mover is playing up, fuel problems, injectors blocked, filter blocked, over heating, needs a diesel Mechanic to have a butcher I would think.
 
Sounds like a engine side failure. Because of the alternater fault I would check all the electrical connections related to it. If it is a stand by set I’m guessing the trickle charge set up will replenish the battery’s and perhaps hide the altonator fault if it’s only ran for short periods
 
Sounds like a engine side failure. Because of the alternater fault I would check all the electrical connections related to it. If it is a stand by set I’m guessing the trickle charge set up will replenish the battery’s and perhaps hide the altonator fault if it’s only ran for short periods
Yes mate it’s a standby set. 24v starter battery which is charged via a 24v rectifier (from the engine control cab).
I see what you’re saying though.
 
Ah yes Dave, couldn't really be electrical, if the Prime mover is playing up, fuel problems, injectors blocked, filter blocked, over heating, needs a diesel Mechanic to have a butcher I would think.
I think that’s a good idea checking the fuel filters etc. It’s in a remote area and probably runs for around 4-5 hours a year, if that
 

Reply to Generator Voltage Failure in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock