So you feel comfortable giving dangerous information about a system you don’t know the details of?

More fool you!

You may call me a fool, not the worst thing I've ever been called although I hopefully still have a few more years in me to better it. Although I am still waiting for you to give a valid reason why the information provided is dangerous?
 
I must admit, l am curious as to why earthing arrangements have to be carefully considered, like I said in my earlier post I have no experience in alternative sources, and thought someone like Tony who seems to know what he's talking about could pass on some knowledge, don't want a lesson just an insight.
 
Too many times have inexperienced electricians connected a centre tapped site generator as a stand by to a permanent supply. Either the generator burns out or if it survives, the neutral has no over current protection making the system dangerous.

Clear disconnection between the DNO and generator protects the DNO operatives against back feeds.

The earthing between the two power sources should be able to be disconnected, again a danger to DNO operatives due to circulating currents.

It’s one hell of a field to enter. I’ve only dealt with small to medium units (15 to 2500KVA) Each needs to be looked at individually to prevent danger due to internal and external conditions.
 
Too many times have inexperienced electricians connected a centre tapped site generator as a stand by to a permanent supply. Either the generator burns out or if it survives, the neutral has no over current protection making the system dangerous.

Clear disconnection between the DNO and generator protects the DNO operatives against back feeds.

The earthing between the two power sources should be able to be disconnected, again a danger to DNO operatives due to circulating currents.

It’s one hell of a field to enter. I’ve only dealt with small to medium units (15 to 2500KVA) Each needs to be looked at individually to prevent danger due to internal and external conditions.

i was under the impression that in a fully auto system they utilise a changeover switch that will swap the supply to the genny when the perminant supply fails.

if i recall don't they use a ups as well for a seamless transfer whie the genny starts up?

edit:

very interesting read ty for website

hmm i asumed most transfer switches were what is described as 4 pole, seems to me anyway to be much better to keep the two supplies seperate using a 4 pole switch.

please correct me if im wrong
 
Last edited:
Too many times have inexperienced electricians connected a centre tapped site generator as a stand by to a permanent supply. Either the generator burns out or if it survives, the neutral has no over current protection making the system dangerous.

Clear disconnection between the DNO and generator protects the DNO operatives against back feeds.

The earthing between the two power sources should be able to be disconnected, again a danger to DNO operatives due to circulating currents.

It’s one hell of a field to enter. I’ve only dealt with small to medium units (15 to 2500KVA) Each needs to be looked at individually to prevent danger due to internal and external conditions.

Tony - I appreciate what your saying in regards to the final connections, loading, earthing, generator type etc but that is not what my initial advice was about, the OP ask what the set-up would be to prevent back feed, this was given and IMO correct, you can comment on that and prove me wrong if that is the case and I'll be the first one to put my hands up, but to make a sweeping statement that all previous information is dangerous is unjustified ( unless of course you do prove me wrong :) ) I was just curious to know how you came to that conclusion?
 
Last edited by a moderator:
Interesting thankyou.

You're welcome. As far as I know that is the code of practice for UK installations although there may be other regs that need consideration.

I see the document I linked to has a copyright notice contained in it. The document isn't hosted on this forum and depending on your location and your local laws, it may, or it may not be legal to download or distribute the document.
 
Tony - I appreciate what your saying in regards to the final connections, loading, earthing, generator type etc but that is not what my initial advice was about, the OP ask what the set-up would be to prevent back feed, this was given and IMO correct, you can comment on that and prove me wrong if that is the case and I'll be the first one to put my hands up, but to make a sweeping statement that all previous information is dangerous is unjustified ( unless of course you do prove me wrong :) ) I was just curious to know how you came to that conclusion?

It's quite simple, without information on the system it's foolish to give advise. Especially as the OP came back with a response to unreliable information.

I worked on private MV networks that fed not only the various plants but also farms and villages on our estate. Farmer Brown revving up his generator was a constant danger due to back feeds.

Sorry, but generators in the wrong hands are dangerous.
 