A

adamw1

easy lads, im doing some diy and iv dug down under the footings to underpin, in one of my sections is a earthing/grounding rod. im only goin down about 80cm, do i have to remove the rod and re-place or can i dig around it? or should a sparky come and sort it out for me? answers on a postcard..
 
It's difficult to say without more info, a couple of photos might help. I would say if the rod shows any signs of becoming loose (even slightly) whilst you're excavating then get a sparky in to relocate it. Also the rod needs to be accessible for visual inspection so if your groundworks will result in the rod ending up being completely buried in earth or concrete it might need moving anyway.
 
You'll also need the rod testing the ensure you're still getting a good earth, a spark will be able to confirm the earthing arrangements for your property as they may have changed over the years and the rod may not have been removed if things have changed.

A photo of the incoming service head would also help.
 
Personally you should stop digging near the rod and have it repositioned.

When you back fill your excavations, there's a chance that the earth around the rod may not be as compacted as before, and could possibly affect the Ra reading of your property.
 

Reply to grounding rods in the Electricians Chat - Off Topic Chat area at ElectriciansForums.net

Similar Threads

Hello. I'll apologize to start with as due to my lack of knowledge on the matter I'm likely to waffle a bit and call everything by the wrong name...
Replies
16
Views
2K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
917
Hi all, first post so go easy! This is for people who are looking for more info on the course and exams and is from my experience of doing the...
Replies
1
Views
3K
Hi Everyone, 1st post here as a DIY-er, I need to run a ground wire from the bottom spindle of my turntable (TT) platter to dissipate electrical...
Replies
9
Views
2K
Hello everyone my name is Tarek, i work as a concert and show lighting operator with over 20 years of experience in this field, so i have gained...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock