Discuss Had an idea, anyone tried it or think it may work? in the UK Electrical Forum area at ElectriciansForums.net

Mattja

-
Reaction score
10
I'll keep the blurb brief for you all!

Old fusebox in bathroom cupboard. No suitable place it could realistically be moved to. Clear signs of corrosion damage (I've cut back the damaged parts and reterminated). Upgrading to CU in a few weeks when client is back from holiday.

My idea is to install a fan pumping air from the adjacent room (dining room end of combined kitchen-dining room) through a duct and into the cupboard to create positive pressure, hoping to stop (or greatly reduce) steam from the shower getting into the cupboard. There's no window in there since it's below street level, so they would always turn the light (and hence the fan) on when using the shower.

P.S. yes there's already a bathroom fan installed as normal
 
Hi - another thought - is it possible to put it on the other side of the wall ? (where your air vent was going? ). I'm guessing the flat is fed via a switch fuse and swa to the board, but in the bathroom ... o_O.
The issue with your +ve pressure idea is that I think the installation would have to be under supervision, as the release from having the correct IP.
Just fyi, the Last Electrician at my home put the CU in a kitchen cupboard. It is accessible (just) but has halved the household tea cup capacity. Shocking !
 
Unfortuntely I can't put it in an enclosure. CU is barely going to fit as it is. If you know of a CU that is rated to at least IPX2 to protect from condensation and complies with amd3 I'd love a link as I've not found one.
 
It should go in a suitable location.

Where it is, is not suitable apparently. It needs to go somewhere more suitable. When you've added you fan thing etc, and when it starts going Pete Tong (which it will), you'll inherit the problem. The problem is not yours, but the owners to bear.
 
@Wilko from my view yes. Client isn't happy with the idea though.

A fan I can hide up in the corner just above the cabinets, but a CU plonked in the middle of the fancy plates and silverware is a little more conspicuous >.<

Thinking I may have to insist upon move it there and hope he's still willing to have it done. Wish me luck on that then.
 
Could you not install a plastic IP rated consumer unit and put it down as a deviation, proving that it is safer, as long as you tighten all the conections up it will a dam site safer than a metal one full of water
 
You are adding an extra,which may have unintended influences.
I presume the cupboard is sealed? ....so you will need two vents,in and out,and decide where they go to and from...

I suppose,it would be a departure....in the same way,as not fitting a metal enclosure,but mitigating the risk of fire,in the new plastic one,by mounting a constant 24 hour video feed of it,to your smartphone,so it can be monitored.;)
 

Reply to Had an idea, anyone tried it or think it may work? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi there, Just about to move into a house with 2 small kids and the wiring/electrics haven't been updated in years (hard to know as it's probate)...
Replies
10
Views
2K
One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K
We are installing a new shower, electric towel rail, light and fan in a bathroom. The existing mains board is a old wylex rewirable. Gas and water...
Replies
32
Views
4K
Hello i've recently just had a re wire done on a three bed semi house, Ive noticed a few things im not 100 percent on ive spoken to the firm that...
Replies
24
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock