I've installed and tested a 4-zone Haes Eclipse fire panel. It is wired up as a two-wire "Sav-wire" system where the sounders are wired with their polarity reversed. This is the first panel of the this type I have installed as so far we have always installed Firesence panels which are no longer available as a 2-wire system.
On initial testing everything was OK. Then after a couple of days it started showing an intermittent "general fault" on one of the zones. Using the panel lights to diagnose the fault suggests a short circuit but there isnt a short circuit - all 4 circuits show about 4 k ohm. If you swap the wires for two zones then the intermittent fault moves to the other zone which seems to indicate it is not a fault with a specific zone on the panel, but is a fault on the circuit for that zone.
The zone circuit has 9 sensors, 5 sounders and 3 call points.
Any ideas for how to isolate the fault?
On initial testing everything was OK. Then after a couple of days it started showing an intermittent "general fault" on one of the zones. Using the panel lights to diagnose the fault suggests a short circuit but there isnt a short circuit - all 4 circuits show about 4 k ohm. If you swap the wires for two zones then the intermittent fault moves to the other zone which seems to indicate it is not a fault with a specific zone on the panel, but is a fault on the circuit for that zone.
The zone circuit has 9 sensors, 5 sounders and 3 call points.
Any ideas for how to isolate the fault?