I've started some work for a new commercial client to add a new 3 phase 32A commando socket to one of their DB's. I've noticed the main distribution board is using Hager MCCBs in the MCB ways (apologies for the poor quality photo). Is this supported as I can't find any documentation saying it is?

Also if it is supported, I'm assuming the MCCBs have been installed the wrong way round.

WhatsApp Image 2025-09-22 at 12.19.24.jpeg
 
I've started some work for a new commercial client to add a new 3 phase 32A commando socket to one of their DB's. I've noticed the main distribution board is using Hager MCCBs in the MCB ways (apologies for the poor quality photo). Is this supported as I can't find any documentation saying it is?

Also if it is supported, I'm assuming the MCCBs have been installed the wrong way round.

View attachment 123581
MCBs are normally domestic and where commercial would be light industrial and office and retail. Though you could see MCCBs there as well.

MCCBs would be Industrial and especially with heavy equipment or any application with higher currents.

I take it this board is supplying industrial equipment? If so no surprises.

MCCBs have higher breaking and higher ratings and also can be adjustable for trip times etc.

I see they they are supplying sub boards therefore it might be the trip times might have been adjusted to suit design criteria, you can only really do that with MCCBs.
 