i have a fuse box with a 32a ring on it and two 6a lighting on it its in a factory and the ring has a few molding machines on it. this CU has a eaton 40A supply on a 6.mm 4c armored.
now i need to install a 32a spa onto the CU.
im a little worried that with the start up from cold on the spa with 6kw heater and the ring main loaded that the 40a eaton would trip.
ive been looking for a 45 or 50 with no avail so do i just attach and hope it will be ok or do i find another make that will fit?
cheers guys thats all the info i have.
now with diversity and the over rating on the mcb ... ... im wondering.
 
If the supply is 3 phase then why would it overload another phase assuming spa is single phase? Why do they want a spa in a factory? Do they have any vacancies there?
 
25A on the spa cycling, 20A on the ring cycling, nothing much on the lights cant see a 40A going any time soon unless the moulding machines are very high draw and already pushing the 32A.
You are looking at it taking 60A for half an hour OK. might just trip on inrush if it is type B.
 
not three phase jumpin jax.
i thought about the sudden rush of power on heat up will take a good few hours to warm.
hot tub in factory thats what i said is it for the staff. lol
they starting up a show room.
 