This is what I do......
First make sure all appliances are unplugged, any fuse spurs turned off (this would give you a 0.26ish result, from reading between the neon)
One crocodile clip on both live conductors, the other on the Neutral conductors. Test. Hopefully >99.9
Repeat test for Live/Earth and Neutral/Earth.
Done. Although you could save time, by doing as what someone said above, using the screw in the MCB, and the busbars. If your really special you can IR test the whole installation at once. Making extra sure, you disconnect any equipment suspect to high voltages.