It’s a old detached house which is a fair few meters away from neighbour. I am stumped atm
So with the gas bond removed there is no other earths connected to the CU earth bar apart from the final circuit earths?
It’s a old detached house which is a fair few meters away from neighbour. I am stumped atm
Not that I can see no
Sorry that’s correct yesSo with the gas bond removed there is no other earths connected to the CU earth bar apart from the final circuit earths?
There is no other earthsSurely you can see the whole of the earth bar? Is there another earth or not? Your answer seems unsure so just need to clarify.
As I can’t find an Earth would you suggest earth rod? Although this zs at db reading is so lowOld properties often have earth's from random sockets to the incoming water ....
just tried that and it wouldn’t pick an Earth up from the casingThat is a lead sheathed cable coming in which should be connected to the ISCO sealing chamber and other ISCO boxes.
Inspect and test the cover of the sealing chamber to see if it is connected to the lead sheath and then test it to see if it gives a good Ze.
Just t
just tried that and it wouldn’t pick an Earth up from the casing
DNO coming on a slow boat from China? that lead time is a disgrace.DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.