I’ve explained. There are final circuits and one 6mm which goes to the gas bond only! Nothing else no main earth nothing. Just the earths from the circuits
 
DNO don’t seem to care! They bassicly told me to put it on a TT system. They can send someone out to see if it can be changed to PME but that’s a 5 week waiting time.

Did you explain to them that there’s an unearthed cast iron cutout with open holes in the top exposing live parts?
The TT/PME answer sounds more like the standard response to asking for an earth connection rather than reporting this situation.
 
the op needs to get DNO in to have a look at it ,if he is in doubt.
test at the cu and test for a earth on old DNO isolators . what's the betting their is a earth some where .ring up Scottish and south Elecs.
 
I've seen it before, inside the cast iron isolators theirs a rewireable fuse, what your seeing is a split supply for another building aswell as yours. Back in the 50's it was also acceptable to use the gas as the earth. The meter fitter wants reporting, but it is upto the electrician to give a earth. is it a rural location?
 
Did you explain to them that there’s an unearthed cast iron cutout with open holes in the top exposing live parts?
The TT/PME answer sounds more like the standard response to asking for an earth connection rather than reporting this situation.
Yes explained clear as day she just put me on hold and then went on to say they can send someone out in 5 weeks.
 