HELP! SINGLE SOCKET with 2 appliances near miss!
Seeking advice from qualified electricians.

Female, currently home alone with my baby and older child while my partner (construction manager) works away.

SINGLE SOCKET in the kitchen with block style multi plug-> Dishwasher plugged in, also plugged in is a 4 gang extension lead with washing machine (due to being too far away from the main socket) plugged into it, then another 4 gang extension lead plugged into that with the broadband hub plugged in.

WiFi has been went off and noticed washing machine and dishwasher also off.

Block multiplug sparking, removed and noticed the plastic melting.

Called my partner for phone advice, he asked me to look at the fuse; crumbling black plastic around fuse but fuse looked intact. He thinks that the block plug is what failed due to loose connection or the fuse being replaced before perhaps. Told me to plug extension lead (which has another extension lead on it) back into the single socket and continue using, just to not use the melted block adapter.

I have asked that we get an electrician to look at it and find a safer solution than the current one, he is refusing this and making out i am being overly panicked etc. he says just to make me happy he will change the single socket to a double socket and continue running the same appliances and extension lead situation from this.

I’m concerned about this and of course google agrees with me but he says it’s just “guidance” not to do this. Is this socket safe to use at all now? Is his solution of changing to a double socket and continuing to run the extension leads and appliances safe?
I’m happy to insist we get an electrician but need some more reasoning to put forward, he said an electrician would laugh at me for calling for this 🥴
Ultimately, i own the house so I have more of a vested interest in it than he does.

Thanks for your help 😊
 

Attachments

  • IMG_6403.jpeg
    IMG_6403.jpeg
    937.6 KB · Views: 22
  • IMG_6406.jpeg
    IMG_6406.jpeg
    971.4 KB · Views: 22
  • IMG_6402.jpeg
    IMG_6402.jpeg
    959.7 KB · Views: 21
  • IMG_6398.jpeg
    IMG_6398.jpeg
    1 MB · Views: 21
  • IMG_6403.jpeg
    IMG_6403.jpeg
    770.4 KB · Views: 21
  • IMG_6406.jpeg
    IMG_6406.jpeg
    874.5 KB · Views: 23
  • IMG_6402.jpeg
    IMG_6402.jpeg
    1.7 MB · Views: 22
Last edited:
technically, and theoretically, the load on the single socket is limited to the 13A fuse in the first adaptor block.... but thats where the problem lies....
The weight of the block, and any cables hanging from it slowly pull it from the socket, causing it to arc between the socket and the pins of the plug.

There is also the risk that one of your extension leads may not be designed for a high load over a long period of time. Some are only rated for 10A, rather than 13A... and should only have a 10A fuse in the plug.... which has maybe been replaced with a 13 in the past.

It is best for high powered loads to be on individual single sockets... as a double socket may only be rated for 20A between the 2 outlets, rather than 2x13 as you may think.
 
I would not laugh at you.
There are so many safety information leaflets out there that tell you not to plug extension leads into each other for just this reason.
You are likely to overload the socket that supplies this chain of things plugged in.

It looks like it was the socket adapter that failed, however it could have damaged the socket by overheating it.

In the short term, you would be much better to use a 4 way strip type of cable instead of the cube adapter , also, only use 1 high power device at a time. I.e washer or dryer, never both together.
 