How would you answer this Q:
A final circuit is installed using single core pvc insulated cables enclosed in steel conduit. The conduit is used as the cpc. An earth fault loop impedance test identifies that the max permissable Zs has been exceeded. describe:
A) 3 possible faults that may cause the high reading
B) One test that could be performed to verify the reading.


Just blown my mind on so many revision Q's today that my brain has gone into melt down and I have been looking at this Q for so long I have gone blank.
 
I'm only on year 2 however A) as Zs=Ze + (R1+R2). A1) R2- cpc has high resistance at conduit junctions (needs tightening up) or not connected to supply earth A2) Ze- too high may be on TT supply A3) R1- Cable run too long or dodgy connections B) look at results from earlier tests of impediance tests of R1,R2 and CPC that you had to do before ELI and if these were fine then test ELI test at origin of supply to get Ze. If there had been dodgy readings in the earlier tests you wouldn't have done a live ELI test anyway so must be Ze. Do I get a prize?
 
Last edited by a moderator:
1 wrong size bonding conductors, 2 poor terminations on bonding conductors, 3 continuity not being made via a direct path and so a strange parallel path reading being achieved. should do an eart loop impedance test with an impedance tester who this helps
 
Hi
I would just be cautious about the parallel paths suggestion.
I believe that parallel earthing paths would reduce ZS rather than increase it.
Hope this helps

CH
 
High current low impeadance ohmmeter - wander lead method - I think
might be helpful if you could obtain a copy of the practical guide to inspecting and testing available from NIC at about £20.00
 

Reply to Help with 2330 303 Q in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
The purpose of this thread is two-fold: to let you folks see an EICR from someone who's too lazy (or busy) to even bother forging his test...
Replies
15
Views
3K
Hi guys, I'd appreciate the opportunity to pick your brains a bit, and make sure I'm on the right track, please. (Will also be talking to my...
Replies
3
Views
2K
Hi, I am resitting my FICA Underpinning Knowledge test next week and I stuck on a few questions in the mock tests they have on their website. I...
Replies
4
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock