I have a ideal 24 combi in attic. last year during very cold nights the frost stat would kick in and heat the whole house , just because the attic was cold. i had a pipe stst fitted a week or two back by a plumber and every day / night since the CH is coming on / going off. so the pipe stat is working but was is turning the CH on in this mild weather ?
 

UNG

-
Mentor
Esteemed
Arms
Reaction score
5,223
What is the expected function of the pipe stat?

I'm assuming the frost stat is built into the boiler and operates at a temperature preset by the manufacturer
 
OP
P

paul b

DIY
Reaction score
0
What is the expected function of the pipe stat?

I'm assuming the frost stat is built into the boiler and operates at a temperature preset by the manufacturer
hi. the frost stat came with boiler set at 5. the pipe stat is needed to turn the CH off in winter months when the frost stat has turned it on. cos the attic is much colder than the house
 

UNG

-
Mentor
Esteemed
Arms
Reaction score
5,223
hi. the frost stat came with boiler set at 5. the pipe stat is needed to turn the CH off in winter months when the frost stat has turned it on. cos the attic is much colder than the house
So you would risk the boiler freezing and damaging the heat exchanger which would be costly to replace because you are too warm

Without digging into the boiler wiring diagram to verify you might have been better getting a smart thermostat or heating controller that could limit the overnight heating temperature to 8 - 10°C
 
OP
P

paul b

DIY
Reaction score
0
So you would risk the boiler freezing and damaging the heat exchanger which would be costly to replace because you are too warm

Without digging into the boiler wiring diagram to verify you might have been better getting a smart thermostat or heating controller that could limit the overnight heating temperature to 8 - 10°C
what i have said is the CH is constantly coming on NOW when weather is mild (15’) in attic with frost stat set at 5’ so asking what is turning my CH on ?! i am not risking the boiler freezing
 

brianmoooore

-
Esteemed
Arms
Reaction score
5,445
Pipe 'stat and frost 'stat should both be fitted, and connected in series. Pipe stat should be on the return boiler pipe and set at about 5 degrees. There will be some heating of the house, but it should be minimal with the return flow limited to just above freezing.
 
  • Optimistic
Reactions: UNG

UNG

-
Mentor
Esteemed
Arms
Reaction score
5,223
what i have said is the CH is constantly coming on NOW when weather is mild (15’) in attic with frost stat set at 5’ so asking what is turning my CH on ?! i am not risking the boiler freezing
How are you measuring / monitoring the overnight temperature in the loft is the 15°C an actual measured temperature
 

brianmoooore

-
Esteemed
Arms
Reaction score
5,445
The frost stat needs to be fairly close to the boiler, so that it is affected by the heat leaking from the boiler.
The odd bit of panelling near the boiler might help. Not to enclose the boiler, but to protect it from draughts in the attic.
 

brianmoooore

-
Esteemed
Arms
Reaction score
5,445
Three of my boilers are fitted with frost protection. Two are in fairly small outdoor sheds, which become a few degrees above the ambient when the boiler is running, and the third is a standalone outdoor unit, where the frost 'stat is actually inside the boiler casing.
All three prevent the boiler and external pipework from freezing with minimal heating of the property.
 
Last edited:

Reply to Hi I am a house owner in Wales. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

  • Locked
  • Question
Here is my set up. I have 100 amp service coming into my house into the panel box. I have a 50 amp subpanel in my garage fed from the main...
Replies
4
Views
498
Hi, I’m trying to find a frost stat that will facilitate the switch off of mains power 230VAC to both a fish pond pump & UV clarifier (combined...
Replies
1
Views
329
  • Question
Before I pay an electrician to come check my work, I thought it worth a post here. I don't want to pay the cost of a small car for a whole-house...
Replies
0
Views
545
  • Question
Hello, I am asking for a double check on my project before I purchase any electrical parts. My inverter Solark 15k has a built in 200 bus and...
Replies
0
Views
319
  • Question
I have the typical LED on Dimmer switch. All the lights flicker in my house are very inconsistent times. By let me clarify by saying all the...
Replies
0
Views
464
Advertise Here

New Posts (Please Reply)

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Top