God knows why. Installed 20 to 25 years ago by who knows who ?What earth clamp? I thought this was an SWA cable, why is an earth clamp involved in this?
Discuss Hi Ze Reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
God knows why. Installed 20 to 25 years ago by who knows who ?What earth clamp? I thought this was an SWA cable, why is an earth clamp involved in this?
God knows why. Installed 20 to 25 years ago by who knows who ?
You really need to focus on the length of SWA in question. If it was me I would completely strip down all the terminations BOTH ends and also IR from both ends at 500V minimum.
Ze at origin is a good reading