Hi Andy,
i did did not measure those, the eicr has the cooker at 0.43 and the central heating at 1.44.
the eicr has the radial at 0.83, however I recorded the radial at 42 so unsure if the electrician doing the eicr did all but the radial, central heating and cooker by calc.
Those could be worth investigating to see if the high loop readings are consistent across all the circuits that are protected by the RCD. If not then a point of high resistance common to the first three circuits would seem logical. It's not unknown for breakers to be installed incorrectly on the busbar, or for multiple sections of busbar, or even cable links, be used to make up connections between breakers for instance.