Hi all,
I was hoping to sneak in a little job late this afternoon - changing a faulty bathroom pull chord for an outside switch plate. No problems with access. Straight forward enough.
House is almost certainly post 60's. CPC's present in lighting circuit.
Live Zs = open circuit.
R2 test with wander lead from MET to as many lighting JB's in the loft I could find = 60 k ohms.
So there is some sort of reading.
Loose connection?
Back tomorrow so any advice on where to start always appreciated.
It looks like the lights are wired in single line + cpc, looped in an out using every which method you can think of, and a neutral looping around each load.
Like I said - where to start.
There are other circuits available in the loft - I could bridge across from 1 JB to another with some 4.0mm if I have to (I suppose).