hotXbun,

No 3 yes you can share the earth and that is what I would do initially to make the lights safe in the bathroom.

Reg 543.1.2 & Reg 543.1.3 (page 128)which basically means the protective conductor must be sufficient for the worst case.
I would connect with the 6mm T&E cpc.

My house 1967 didn't have cpc to light fittings, only found out when mrs wanted to change the lights in bathroom, I had fitted shower few years previously (long before taking 2330 etc) so I dropped cpc from light into it going with the idea they all meet in cu :-o. Discussed on course. As for regs I decided to do the 2380-10 instead of 2380-20 made me read regs more and thats how I found it, since got adaptable box in loft with earth bar and connected all upstairs lights this way.

BTW the ESC has a guide for cu change that says if no earth and class I fittings then fit RCD, could be easier.

Is the shower RCD protected?
 
Last edited by a moderator:
hotXbun,

No 3 yes you can share the earth and that is what I would do initially to make the lights safe in the bathroom.

Reg 543.1.2 & Reg 543.1.3 (page 128)which basically means the protective conductor must be sufficient for the worst case.
I would connect with the 6mm T&E cpc.

My house 1967 didn't have cpc to light fittings, only found out when mrs wanted to change the lights in bathroom, I had fitted shower few years previously (long before taking 2330 etc) so I dropped cpc from light into it going with the idea they all meet in cu :-o. Discussed on course. As for regs I decided to do the 2380-10 instead of 2380-20 made me read regs more and thats how I found it, since got adaptable box in loft with earth bar and connected all upstairs lights this way.

BTW the ESC has a guide for cu change that says if no earth and class I fittings then fit RCD, could be easier.

Is the shower RCD protected?

Thanks for that :) At the moment the CU only has RCDs on the power circuits and I will be modifying it to include proper RCD protection to all circuits. I've been chatting with client and we've decided to investigate and see if I can take a dedicated 1.5mm T&E from the CU in the garage and see what problems will be encountered. Also I am going to re-connect the shower supply with a 17th edition junction box - all secure and tidy - before testing it out.

Having looked at section 543 - Protective Conductors, I'll certainly consider using this as a reference so thanks for pointing that out
 