This is my guess, on the basis you are given two mains cables, a 16A with 5 conductors and a 32A with 3 conductors, and you are supposed to use one or the other.
The hob has provision for 3 phase connection, likely designed for sale in Europe as well as UK.
Since you probably have a single phase supply, use the 32A lead and connect together L1, L2, L3 at the hob, probably with a supplied plate, as per instructions
Alternatively tell us the make and model and we can check!