Hi I have go a bit of home work but im unsure about one of the questions it says

You have been tasked by your supervisor to install a new A3 circuit in the store room for a general workers to use, you go into the distrobution room and see it is a 3phase board with bs 3036 fuses, are you able to comple the task asked by the supervisor, if so explain why?

I think it will be ok to install a A3 circuit on 3036 fuses aslong as the sockets are rcd protected by a rcd either inline or incorporated into the socket.

Would you say that was ok
 
yes, but if cables are buried inn wall/s < 50mm deep. 522.6.101 applies also.
 
Hi the picture at the back looks like every thing is surface mounted in conduit do it wont be in a wall
 
Maybe check these as well :smiley2:

On site guide ... 7.2.4 (page69)

BS7671 BGB 433.1.101 (page81)
 