hot tub in garage (diversity)

Discuss hot tub in garage (diversity) in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
house supply 100A tns 32A mcb feeding garage(10mm swa buried ) 100A board.. currently with lights on 6A and sockets on 20A ....customer wants massive hottub installed in garage ....problem is manual says requires 2 x 32 A supply for tub ........any suggestions ?
 
Do you have a picture? 2 x 32amp might mean L&N conductors to the unit.

If it is only 32amp, upgrade the MCB size to the garage ( if possible, assessing conditions )

Then you can run the original stuff + Hottub
 
It's hard to tell what is actually being said in the instructions. 2 separate cables or 2 separates cores? Are you an electrician?
I wouldn't imagine the thing needs 2 x 32amp supply. It's only a couple of pumps and a heating element.
But OP said 'massive' hot tub......could have 2x 6kw elements.
I think we need kw rating from the OP.
 
I have come across a hot tub with 2 supplies needed, was in garden of a scrap metal dealer who fancied himself as a bit of a local celeb living the big life. It needed 2 cables, cant remember what rating MCB but each cable did different things, one supply cable was the heating system and the other did pumps, sound and lights... the hot tub was like a mini swimming pool and could take several large adults or in his case young ladies charging by the hour! only learned this as he wanted sockets down by his BBQ area and had to work out why the hot tub had two supplies in the consumer unit for outdoors as it confused me and then boss no ends. I still do not see point of underwater speakers!

Just a thought on the op's post is that the hot tub could be a foreign model thats been imported as a lot of the US models are designed for multiple wires and often have 2 lives one neutral and one earth, its less likely on Uk models unless very large with separate spa/hot tub compartments within the hot tub as in my example.
 
Last edited:
.........hot tub could be a foreign model thats been imported as a lot of the US models are designed for multiple wires and often have 2 lives one neutral and one earth, its less likely on Uk models unless very large with separate spa/hot tub compartments within the hot tub as in my example.
USA alleged 240 gear - only insulated to 120v !

Inverted 120V phases (or similar, whatever correct terms are)
120-0-120 where 0 = Neutral
 
black diamond spas

img042.jpg
 
I would tell them to better spend the money on a taste and style refining course they will then realise said hot tub and current lifestyle adornments need addressing.
 

Reply to hot tub in garage (diversity) in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock