devonsparky

This is a follow up to a thread I started yesterday.

I have been working all day installing a hot tub situated outside on a patio slabbed deck.

Contrary to what I was told, it was TN-C-S supply so here is how I have wired it.

  • From Henly blocks - 25mm tails to a one way board (Main Sw RCCB - 50A MCB)


  • 10mm 3 core SWA from board to 63A rotary isolator and from rotary isolator to hot tub


  • Earth rod with 10mm G/Y back to one way board and then used one core as an earth to the hot tub and connected the armour to the earth bar too.



Time beat me today so I have not connected into the Henly blocks yet and tested .......................... Is this how you guys would have done it. 10 years in the game and an approved electrician and it's still nice to get feedback off of this forum !! ha ha
 
All the ones ive installed ive installed on a TNCS supply if thats on the house and they are fibre glass and the only metalic parts are within the TUB none have integrated RCD's, main switch RCD and 40 amp MCB if you get a neutral fault then this will cause an imbalance and trip the RCD , in the area i am if you can get an earth rod in more than 300mm you'll be lucky , non of the manufacturers instruction have stated that they require an RCD and i understand about exporting the earth , bit like roding a wooden garden shed supply
 
All the ones ive installed ive installed on a TNCS supply if thats on the house and they are fibre glass and the only metalic parts are within the TUB none have integrated RCD's, main switch RCD and 40 amp MCB if you get a neutral fault then this will cause an imbalance and trip the RCD , in the area i am if you can get an earth rod in more than 300mm you'll be lucky , non of the manufacturers instruction have stated that they require an RCD and i understand about exporting the earth , bit like roding a wooden garden shed supply

Dont just think of the tub construction material when talking about Class 11, you have pumps and heaters, then think what will pass through them, ..yes water, ...but not just your standard tap water, the water will be treated with chemicals to correct Ph values and others for disinfection to keep it crystal clear, such as Bromine, Algaecide, flocculates, etc etc... Which i would think, will make the water far more conductive than your standard water will be....
 
Last edited by a moderator:
Dont just think of the tub construction material when talking about Class 11, you have pumps and heaters, then think what will pass through them, ..yes water, ...but not just your standard tap water, the water will be treated with chemicals to correct Ph values and others for disinfection to keep it crystal clear, such as Bromine, Algaecide, flocculates, etc etc... Which i would think, will make the water far more conductive than your standard water will be....

Blinking good point E54. Water on its own, rubbish conductor.
 
All the ones ive installed ive installed on a TNCS supply if thats on the house and they are fibre glass and the only metalic parts are within the TUB none have integrated RCD's, main switch RCD and 40 amp MCB if you get a neutral fault then this will cause an imbalance and trip the RCD , in the area i am if you can get an earth rod in more than 300mm you'll be lucky , non of the manufacturers instruction have stated that they require an RCD and i understand about exporting the earth , bit like roding a wooden garden shed supply


Its not just about a fault on the tub, you should TT a hot tub, its all about the potential difference between true earth and the MET (PME)

Its the failure of the PME thats the worry here,

Plus class 1 fittings in and around the tub could be a problem.

personally i would TT a hot tub
 
yes i do understand so why are we using PME at all because if you loose the supply neutral in a house that has a shower above the a cast iron bath then you have an even worse scenario every piece of bonded metal will become at a potential of around 110 volts so realisticall every PME installation shold be TT just in case
 
Its not just about a fault on the tub, you should TT a hot tub, its all about the potential difference between true earth and the MET (PME)

Its the failure of the PME thats the worry here,

Why? because 1 in ten million have temporarily lost the neutral that is subsequently fixed pronto?

Plus class 1 fittings in and around the tub could be a problem.

personally i would TT a hot tub

So you prefer to rely on a device thats proven to be unreliable and subject to high failure rates (the RCD) for disconnection! Theres a lot more chance (probably several orders higher) of the RCD failing than the PME neutral being lost.


Don't get me wrong I am not a fan of PME (TNS all the way) but .... the logic puzzles me. Loss of neutral is unheard of. And fixed quickly the miniscule few times it happens. RCD failure is rife and often never checked, fixed or found. Especially when they're fitted by a "friend" that has 'acquired' the board and RCD and has no registration, invoice, and more importantly, test equipment. Changed a few things for a mate who had the board changed 8 years ago, as above, RCD was kaputt. Probably never worked. How would we know? It was never tested.
 
Last edited by a moderator:
So you prefer to rely on a device thats proven to be unreliable and subject to high failure rates (the RCD) for disconnection! Theres a lot more chance (probably several orders higher) of the RCD failing than the PME neutral being lost.


Don't get me wrong I am not a fan of PME (TNS all the way) but .... the logic puzzles me. Loss of neutral is unheard of. And fixed quickly the miniscule few times it happens. RCD failure is rife and often never checked, fixed or found. Especially when they're fitted by a "friend" that has 'acquired' the board and RCD and has no registration, invoice, and more importantly, test equipment. Changed a few things for a mate who had the board changed 8 years ago, as above, RCD was kaputt. Probably never worked. How would we know? It was never tested.

How would you know if the Earth was lost on a TN-S? That's one advantage of PME, the DNO are alerted to it.

Each system come's with risk, non are infallible.

Broken PEN'S, it hapens, quite rare

RCD'S failing, it happens, more down to not testing the RCD quarterly or the system to which it connects to than the RCD itself.

TN-S loss of Earth, it happens, though very little TN-S in most area's now, certainly Domestic anyhow.
 
Hi Chr!s

good point re loss of earth on TNS. Not sure. Assume most losses would be because cable is severed or damaged, isn't the outer usually the earth on TNS?

I'm just a cynic and suspect they dropped the idea of having 3 hard lines back to the sub station as it is (clearly) cheaper to have 2 instead.... all about money.

I agree, nothing is infallible.

Not sure about the quarterly testing. I have come across a few that operate satisfactorily on the test button, but do not operate when tested (ramp, x1, etc) and have been replaced). So as mentioned, nothing is infallible including the test button!

TNS a dying breed.

Don't know much about the construction, etc between a house and substation of a TNS cable. Would love to though!:D
 

Reply to Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock