Hi

Arrived at a portable, metal home. I say that. Its been made out of a shipping container to get around local planning on someones property. It had been signed off by a sparks, so i am told. The earth rod has been Installed in the lake with the top a few feet out of the water near a jetty. No lug, and a very rusty bolt holding it together. Not Conducted an EFLI test yet and i will be installing a new rod out of the lake and installing a proper inspection box. But... they swim in this lake in the summer. So what would be a safe Distance away from the lake for me to install please?

Thanks
 
Regulation 542.2.7 prohibits an object in water being used as an earth electrode.

However, I don't see off-hand what would be a safe distance. Treating the lake as a swimming pool would suggest 3.5m from the high water point as being outside of zone 2 (e.g. Figure 702.2 in the 18th edition page 251) so without any better guidance that would be my best guess.
 
Just as close as possible to the 'building' supply, at the side of the container. If need be, a deep drill down for a decent Ra.
Just because someone swims in it, I can't see how you can contemplate comparing a natural lake with a swimming pool.
 
Got any pictures? Did the lady of the lake put it there?
Regulation 542.2.7 prohibits an object in water being used as an earth electrode.

However, I don't see off-hand what would be a safe distance. Treating the lake as a swimming pool would suggest 3.5m from the high water point as being outside of zone 2 (e.g. Figure 702.2 in the 18th edition page 251) so without any better guidance that would be my best guess.
Got any pictures? Did the lady of the lake put it there?

Haha, no. Funny white rabbit keeps following me round though!

I can’t provide pics sorry, the guy is very Private. Suffice to say its clad in cedar, has hot n cold running water and toilet etc. I am getting 6 ohm on the earth stake and 1ohm on the armoured. Armouring is isolated. It is Also 3 phase.
 
Regulation 542.2.7 prohibits an object in water being used as an earth electrode.

Depends how you read it. I think it is supposed to prohibit relying on the immersion in a body of water to complete the circuit, e.g. a submersible pump casing that is not embedded in the ground cannot be expected to 'earth itself.' A rod passing through water on its way to being suitably embedded might be compliant, perhaps without the swimming factor in this case.
 

Reply to the thread, titled "How close to a lake can i install an Earth Electrode?" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk

Thread Information

Title
How close to a lake can i install an Earth Electrode?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
John-,
Last reply from
Lucien Nunes,
Replies
6
Views
2,668

Advert

Back
Top