Hi,

Just a quick question (hopefully), just put a new dishwasher in and about 15 mins into its cycle the RCD on a 16th ed. split load board covering all the sockets in the house, oven, etc. tripped, I was also running the washing machine and tumble dryer at the same time as well as other stuff that hangs off the RCD fridges, general electronics etc.

The water in the dishwasher was warm but not hot so it clearly had already started heating, so not like the heater had just clicked on and tripped it. Did a quick IR test on the dishwasher at the plug although I know thats probably not that useful as it won't cover all the components, but the reading was fine. So thought maybe its just cumulative leakage, well I checked this on the tails in the meter box, it was varying quite a bit between 15-23mA i imagine depending on cycles of appliances and stuff, but of course that's total leakage on every circuit in the house not just what's going through the rcd that tripped. So anyway I figured out this new dishwasher appears to have a consistent leakage current of around 4-5mA, just wondering really wether this is normal especially for a new dishwasher?
Seems a lot when you think the recommended limit for a 30mA RCD is just 9mA?
Cheers guys
 
Hi,

Just a quick question (hopefully), just put a new dishwasher in and about 15 mins into its cycle the RCD on a 16th ed. split load board covering all the sockets in the house, oven, etc. tripped, I was also running the washing machine and tumble dryer at the same time as well as other stuff that hangs off the RCD fridges, general electronics etc.

The water in the dishwasher was warm but not hot so it clearly had already started heating, so not like the heater had just clicked on and tripped it. Did a quick IR test on the dishwasher at the plug although I know thats probably not that useful as it won't cover all the components, but the reading was fine. So thought maybe its just cumulative leakage, well I checked this on the tails in the meter box, it was varying quite a bit between 15-23mA i imagine depending on cycles of appliances and stuff, but of course that's total leakage on every circuit in the house not just what's going through the rcd that tripped. So anyway I figured out this new dishwasher appears to have a consistent leakage current of around 4-5mA, just wondering really wether this is normal especially for a new dishwasher?
Seems a lot when you think the recommended limit for a 30mA RCD is just 9mA?
Cheers guys
I believe the product standard for dishwashers allows up to 5mA. You might find leakage drops slightly over time if the dishwasher has been in a warehouse for a while.

How about an upgraded CU with RCBO's!
 
I believe the product standard for dishwashers allows up to 5mA. You might find leakage drops slightly over time if the dishwasher has been in a warehouse for a while.

How about an upgraded CU with RCBO's!
Ah brilliant thank you, I'll run it on the hottest cycle a couple of times to drive any moisture out and see if the reading improves at all.

And yes that is most certainly on the to do list just not really been rushing to do it as the RCD has been swapped to a type A and lighting circuits been put on RCBOs by someone I'm guessing to pass an eicr so all the important stuff is appropriately RCD protected, but clearly cumulative leakage can be an issue!
 
Ah brilliant thank you, I'll run it on the hottest cycle a couple of times to drive any moisture out and see if the reading improves at all.

And yes that is most certainly on the to do list just not really been rushing to do it as the RCD has been swapped to a type A and lighting circuits been put on RCBOs by someone I'm guessing to pass an eicr so all the important stuff is appropriately RCD protected, but clearly cumulative leakage can be an issue!
The total leakage current from all devices on a circuit protected by a 30mA RCD should ideally not exceed 9ma.
 
The total leakage current from all devices on a circuit protected by a 30mA RCD should ideally not exceed 9ma.
Yes, which it looks like my circuits on the rcd side probably exceed, I only clamped round the main tails rather than the rcd tails as it was quicker but based on my board layout its highly likely that most of the leakage will have been from the rcd side, i doubt two lighting circuits would be responsible for much. Although I have to say this is only the second time I've experienced nuisance tripping, and indeed the dishwasher has been absolutely fine since.

Just out of interest, if you were doing an eicr or checking leakage before adding a new circuit how would you get an accurate reading, clearly its impractical to run all the appliances on all the circuits while also hoping they're at their most leaky state when you happen to look at the clamp meter?
 
Yes, which it looks like my circuits on the rcd side probably exceed, I only clamped round the main tails rather than the rcd tails as it was quicker but based on my board layout its highly likely that most of the leakage will have been from the rcd side, i doubt two lighting circuits would be responsible for much. Although I have to say this is only the second time I've experienced nuisance tripping, and indeed the dishwasher has been absolutely fine since.

Just out of interest, if you were doing an eicr or checking leakage before adding a new circuit how would you get an accurate reading, clearly its impractical to run all the appliances on all the circuits while also hoping they're at their most leaky state when you happen to look at the clamp meter?
An Eicr is for the safety and condition of the fixed electrical installation.
 
543.7.1.1
Equipment having a protective conductor current exceeding 3.5 mA but not exceeding 10 mA, shall be either permanently connected to the fixed wiring of the installation without the use of a plug and socket-outlet or connected by means of a plug and socket-outlet complying with BS EN 60309-2.
So an appliance with a 13 amp plug should not exceed 3.5 mA.

But in the main, we look at installation resistance which uses DC not AC, One meg ohm is normally considered the limit, capacitive and inductive linking can mean the AC leakage is over the DC measurement, but my whole CU last time I checked was around 8 mA, and that is spread across 14 RCBO's.
 
So an appliance with a 13 amp plug should not exceed 3.5 mA.

But in the main, we look at installation resistance which uses DC not AC, One meg ohm is normally considered the limit, capacitive and inductive linking can mean the AC leakage is over the DC measurement, but my whole CU last time I checked was around 8 mA, and that is spread across 14 RCBO's.

Just had occasion to go around measuring EL (with a bog standard EL clamp meter). Reason was getting a mild belt when re-wiring the PE from a battery inverter backup supply output. I'd wired the (de-energised) inverter back up, having changed its original crappy plastic mini CU for a steel one (just for peace of mind). I'd dead tested the inverter "emergency power supply" (EPS) cable before doing this. Nothing was awry.

Fitted the new mini-CU, everything connected except the PE wire from the CU case to the earth block. Doing this gave me a small belt from the case of the new CU then a small spark when I poked the PE into the MET. The grid supply to the inverter was live, and the PE from that stayed connected to the MET. I didn't touch the grid side, my assumption (false, it seems) was that with the grid present the EPS would be dead. Dead testing confirmed this, yet I still got a belt.

Next odd thing was that I found the inverter grid supply RCBO (a 32A DP Fusebox Type A) had tripped. Implying it'd seen close to 30mA imbalance. I tightened all the connections up, reset the inverter RCBO and then had a look at leakage currents. My thinking was there might be a problem with the inverter.

The inverter EL was 3.8mA. I pulled the cover off the main CU and started measuring the EL on every circuit (the CU is a fairly recently installed all-DP-RCBO jobbie). Surprised to see how much EL there was on the rings, air source heat pump, air con, cooker, the solar inverter (separate from the battery inverter I was fiddling with) and a couple of radials feeding a water pump and sewage treatment plant. The EV charge point was only a wee bit lower.

Total EL for the installation was just over 30mA. Fluctuated a bit though. The installations TT, so has a 100mA Type S on the incomer. No individual RCBO was more than the 3.8mA for the battery inverter, though the solar inverter was very close.

TBH I've never looked closely at EL currents, unless there's been a fault. Means I'm not sure if what I'm seeing is normal or not. The installation's never had any nuisance trips (apart from me tripping the battery inverter RCBO earlier). The date on the label shows it was installed in 2023. The EIC is thin on detail. The installer seems to have done the bare minimum, TBH. I suspect they may not have been the best, not least because of the plastic CU used for the battery system backup supply (and some pretty poor workmanship).

My experience is ancient. Did my C&G in 1976. Not worked as a sparks in over 40 years. Did this job as a favour for a pensioner friend. Anyone have any view as to whether the figures I'm seeing are reasonable or not, please? In my day we had no way to measure stuff like this easily. We relied on an Avo and a Megger!
 
Last edited:
Diffrence line neutral 8 Feb 24 reduced.jpg
This is my non UPS supply, the UPS does not go through the consumer unit, and the inverter has a relay which earths the neutral when grid power is lost, and there is an earth rod as well as the TN-C-S earth so still earthed when grid supply fails.
 
View attachment 124652 This is my non UPS supply, the UPS does not go through the consumer unit, and the inverter has a relay which earths the neutral when grid power is lost, and there is an earth rod as well as the TN-C-S earth so still earthed when grid supply fails.


Thanks. Sounds a similar setup. The installer ran 6mm²from the main CU to the inverter (adding a 32A DP RCBO to the main CU). Then there's a run of 4mm² from the inverter EPS to a new, smaller, plastic CU. The house lights and some other essential stuff have been shifted to this new CU. This inverter keeps the EPS, and hence the small CU, live all the time, so works like a UPS. The installation's TT, not that I can see that making a difference. I did check to see if the rod was OK. Seems to be, got an Ra of 27 ohms, so pretty good (clay soil here, though).

I was just swapping out the plastic mini CU for a steel all-RCBO one to match the main CU. No idea why the installer fitted a plastic one. Date on the label's 2021 (I was mistaken when I wrote 2023 earlier), so well after the regs changed. The friend was worried about the fire risk. Not convinced that mandating steel CUs fixes that. The fire problem's almost always someone not having torqued up terminals properly, IMHO.

I've now done a bit of reading up on leakage. Max for fixed Class 1 kit is supposed to be 3.5mA. Not sure how accurate my clamp meter is on the 200mA range, though. Seems the interference filtering used with modern switched mode stuff always has some inherent earth leakage. Apparently it's the capacitors that shunt common mode interference to earth that cause most of it. With inverters I've also read that there can be capacitive coupling within the transformer that adds a bit. Seems normal to have a few mA per appliance. No doubt the interference filtering in an inverter will be fairly hefty.
 
Last edited:
Thanks. Sounds a similar setup. The installer ran 6mm²from the main CU to the inverter (adding a 32A DP RCBO to the main CU). Then there's a run of 4mm² from the inverter EPS to a new, smaller, plastic CU. The house lights and some other essential stuff have been shifted to this new CU. This inverter keeps the EPS, and hence the small CU, live all the time, so works like a UPS. The installation's TT, not that I can see that making a difference. I did check to see if the rod was OK. Seems to be, got an Ra of 27 ohms, so pretty good (clay soil here, though).

I was just swapping out the plastic mini CU for a steel all-RCBO one to match the main CU. No idea why the installer fitted a plastic one. Date on the label's 2021 (I was mistaken when I wrote 2023 earlier), so well after the regs changed. The friend was worried about the fire risk. Not convinced that mandating steel CUs fixes that. The fire problem's almost always someone not having torqued up terminals properly, IMHO.

I've now done a bit of reading up on leakage. Max for fixed Class 1 kit is supposed to be 3.5mA. Not sure how accurate my clamp meter is on the 200mA range, though. Seems the interference filtering used with modern switched mode stuff always has some inherent earth leakage. Apparently it's the capacitors that shunt common mode interference to earth that cause most of it. With inverters I've also read that there can be capacitive coupling within the transformer that adds a bit. Seems normal to have a few mA per appliance. No doubt the interference filtering in an inverter will be fairly hefty.

Re the above. I'm an idiot. The 3.8mA leakage I was reading was the inverter PLUS the "essential services" stuff run from the mini-CU. This included the lighting circuits, a well water pump, a sewage treatment plant and few "emergency power" outlets on a 16A radial.

Checked again and with all the RCBOs in the mini CU off the earth leakage drops to about 1mA. Main culprit is the sewage treatment plant, and a bit over 1.5mA.

Chap reports all's working just fine. We gave it a test this morning my isolating the supply at the incomer. Sure enough everything not run off the mini CU went off. No backfeed to the consumer side of the isolator. No issues with a floating neutral from the inverter either. Must have an internal N to PE relay.

Much better than an electric car charger I looked at a few weeks ago. That was bidirectional and the installer had fed the emergency supply from the car to a standard ATS, the sort you'd use with a genset for backup. Snag was the car obviously had no means of providing a PE. The house was TN-C-S. In emergency power mode the house supply was about 115V from earth on both line and neutral. As the ATS was one of the slow, motor-driven jobbies, the fix was to add a relay powered off the car side to link N and PE. Seemed to fix the problem. Not idea because if the supply fails then there has to be a 50/50 chance that the PEN has broken, rather then the line. Could mean no effective earthing. Impossible to add an extra rod though. No where to put one away from the influence zone of other services.
 

A nice article. The Schneider link inside this article amplifies the topic more and there is a useful flowchart.

The dashes are: the iet.org

With no space between the and iet.


Very useful article, thanks. I like that it gives a list of practical max EL currents for a range of everyday kit. Surprisingly high for a heat pump, by way of example:

The amount of leakage current will vary according to the type of equipment. The IEC 60335 series of Standards provides requirements for different types of products:
  • Fixed PC workstation - 2 mA
  • Printer - 1 mA
  • Photocopier - 1.5 mA
  • Laptop - 0.5 mA (with EMC filter)
  • Grills, toasters/portable cooking appliances - 0.75 mA (earthed metal)
  • Fridges - 1.5 mA (class I)
  • Dishwasher - 5 mA
  • Hobs, ovens - 1 mA or 1 mA/kW of rated power
  • Washing machine - 5 mA
  • Tumble dryer – 5 mA
  • Electric heat pumps - 10 mA (accessible to public)
  • Floor heating - 0.75 mA or 0.75 mA/kW of rated power
 
Very useful article, thanks. I like that it gives a list of practical max EL currents for a range of everyday kit. Surprisingly high for a heat pump, by way of example:
High EL for heat pump most likely due to inverter drives for compressor motor and fan motor. Always worth checking the type of RCD the manufacturer of a Heat Pump specifies in its installation instructions.
 