Hi all, I am newly qualified with ~1 year experience and this is my first post here. It's a question that's stumped me because I'm not sure how to provide RCD protection here due to the arrangement of supplies going to the consumer unit. I will provide information below but please correct me if I'm wrong.
Context:
Its a top floor flat of a complex and there are two supplies feeding the consumer unit coming from the electrical riser which is around 10-15m from the flat itself. The supplies to the two main switches are as follows: main switch (a) is peak supply and main switch (b) is off peak. BOTH line conductor tails emerge from a single meter and as far as I know this is ok as some meters can be dual tariffs.
I have included photos of the arrangement of the supply meter, supplier isolator and tails along with a photo of the inside of the consumer unit. Unfortunately I didn't manage to get a photo of the additional switchgear located in the riser cupboard (to the left of the meter) and I don't know what it is called. Instead I have drawn (tried to the best of my ability) the wiring arrangement and what this switchgear looked like.
Problem:
As the diagram and photos show, the peak and off peak line conductors enter the consumer unit and feed their respective main switches and then final circuits fed accordingly. The issue is that there is a single neutral tail feeding the peak main switch and then a branch of conductor is fed from incoming main switch (a) to incoming main switch (b) as the neutral branch (shown as black wire in both photo and diagram).
I am not sure where to place an RCD across this installation to provide RCD protection to the sockets and luminaires at a very minimum to comply with regs.
If I have a front end RCD (not ideal) then this will trip when the off peak supply kicks in because the vector sum of current IN and current OUT will be imbalanced by the shared neutral.
I'm a little stumped and any information or advice would be really helpful. Thanks in advance.
Context:
Its a top floor flat of a complex and there are two supplies feeding the consumer unit coming from the electrical riser which is around 10-15m from the flat itself. The supplies to the two main switches are as follows: main switch (a) is peak supply and main switch (b) is off peak. BOTH line conductor tails emerge from a single meter and as far as I know this is ok as some meters can be dual tariffs.
I have included photos of the arrangement of the supply meter, supplier isolator and tails along with a photo of the inside of the consumer unit. Unfortunately I didn't manage to get a photo of the additional switchgear located in the riser cupboard (to the left of the meter) and I don't know what it is called. Instead I have drawn (tried to the best of my ability) the wiring arrangement and what this switchgear looked like.
Problem:
As the diagram and photos show, the peak and off peak line conductors enter the consumer unit and feed their respective main switches and then final circuits fed accordingly. The issue is that there is a single neutral tail feeding the peak main switch and then a branch of conductor is fed from incoming main switch (a) to incoming main switch (b) as the neutral branch (shown as black wire in both photo and diagram).
I am not sure where to place an RCD across this installation to provide RCD protection to the sockets and luminaires at a very minimum to comply with regs.
If I have a front end RCD (not ideal) then this will trip when the off peak supply kicks in because the vector sum of current IN and current OUT will be imbalanced by the shared neutral.
I'm a little stumped and any information or advice would be really helpful. Thanks in advance.