Hi all, I am newly qualified with ~1 year experience and this is my first post here. It's a question that's stumped me because I'm not sure how to provide RCD protection here due to the arrangement of supplies going to the consumer unit. I will provide information below but please correct me if I'm wrong.

Context:

Its a top floor flat of a complex and there are two supplies feeding the consumer unit coming from the electrical riser which is around 10-15m from the flat itself. The supplies to the two main switches are as follows: main switch (a) is peak supply and main switch (b) is off peak. BOTH line conductor tails emerge from a single meter and as far as I know this is ok as some meters can be dual tariffs.

I have included photos of the arrangement of the supply meter, supplier isolator and tails along with a photo of the inside of the consumer unit. Unfortunately I didn't manage to get a photo of the additional switchgear located in the riser cupboard (to the left of the meter) and I don't know what it is called. Instead I have drawn (tried to the best of my ability) the wiring arrangement and what this switchgear looked like.

Problem:

As the diagram and photos show, the peak and off peak line conductors enter the consumer unit and feed their respective main switches and then final circuits fed accordingly. The issue is that there is a single neutral tail feeding the peak main switch and then a branch of conductor is fed from incoming main switch (a) to incoming main switch (b) as the neutral branch (shown as black wire in both photo and diagram).

I am not sure where to place an RCD across this installation to provide RCD protection to the sockets and luminaires at a very minimum to comply with regs.

If I have a front end RCD (not ideal) then this will trip when the off peak supply kicks in because the vector sum of current IN and current OUT will be imbalanced by the shared neutral.

I'm a little stumped and any information or advice would be really helpful. Thanks in advance.
 

Attachments

  • Image (1).jpg
    Image (1).jpg
    161.8 KB · Views: 133
  • Image.jpg
    Image.jpg
    146.2 KB · Views: 102
  • image (1).png
    image (1).png
    83.8 KB · Views: 88
I'm not keen on that isolator not isolating the off peak as well, new Consumer Unit I think if you need (RCD) Residual Current Device protection?
As westward says the mem rcd pods are super expensive like £100 each
 
I'm not keen on that isolator not isolating the off peak as well, new Consumer Unit I think if you need (RCD) Residual Current Device protection?
As westward says the mem rcd pods are super expensive like £100 each
How would you go about ensuring both supplies can be isolated, can the customer contact the supplier and ask them to fit another isolator?

Also, if a brand new board were fitted, would the neutral branch from main switch (a) to main switch (b) cause any effects on the functioning of RCBOs? In my mind this shouldn't be an issue as the individual RCBO is only monitoring the imbalance of current across the final circuit live and neutral and wouldn't register any current imbalance across the main switch.
 
That consumer unit is what's known as dual tariff there is nothing wrong with it nor it's supply. Any RCD or RCBO downstream of the "shared" neutral will not be affected.
 
The isolator at the meter cannot be relied on. 132.14.2 would be the relevant reg:

...
Any linked switch or linked circuit-breaker inserted in an earthed neutral conductor shall be arranged
to break all the related line conductors.


The isolator at the meter opens the neutral and the 24hr line, but leaves the off-peak line closed. If this was used as the sole means of isolation, then during off-peak hours, 230V would appear at the off-peak line.

Not only that, it is highly likely the whole installation - off-peak and 24hr, line and neutral - would also be at 230V. They would all be connected through equipment and the neutral connecting both sides of the board, but have no return path for the current as the neutral is open at the isolator.

Really it needs an isolator that links all 3 poles, or the 2-pole isolator changing for henley blocks.

In answer to your original question, the two 2-pole switches in the CU could be replaced with RCDs - these are available second hand on ebay, and are not too expensive, certainly much cheaper than RCBOs. It's not ideal, as you'll lose pretty much everything if there is a fault, but it may be an option if your customer doesn't have the budget for a CU change.
 
The isolator at the meter cannot be relied on. 132.14.2 would be the relevant reg:

...
Any linked switch or linked circuit-breaker inserted in an earthed neutral conductor shall be arranged
to break all the related line conductors.


The isolator at the meter opens the neutral and the 24hr line, but leaves the off-peak line closed. If this was used as the sole means of isolation, then during off-peak hours, 230V would appear at the off-peak line.

Not only that, it is highly likely the whole installation - off-peak and 24hr, line and neutral - would also be at 230V. They would all be connected through equipment and the neutral connecting both sides of the board, but have no return path for the current as the neutral is open at the isolator.

Really it needs an isolator that links all 3 poles, or the 2-pole isolator changing for henley blocks.

In answer to your original question, the two 2-pole switches in the CU could be replaced with RCDs - these are available second hand on ebay, and are not too expensive, certainly much cheaper than RCBOs. It's not ideal, as you'll lose pretty much everything if there is a fault, but it may be an option if your customer doesn't have the budget for a CU change.
Thanks for the responses.

Yep, you're right - the isolator does nothing to disconnect the off-peak supply but at the meter position the installation has two lines emerging and one neutral. Does this mean splitting the neutral into two via a henley block to supply the off-peak isolator with a complete set of tails? I'm not sure how to achieve proper isolation here.

Additionally, to your point about front end RCDs, yes they are not ideal as it knocks out power to the whole flat in case of fault but I am more worried out the imbalances of currents once the off peak supply is triggered which would cause the RCD to trip if it were installed to replace main switch (a).

In any case, I think I can bring the customer around to a board change - I've tried to justify a cheaper solution but it seems more trouble than necessary. My main concern now is isolation at the meter, wondering, can I/customer ask the supplier to address this themselves as its their equipment?

TIA
 
Hi all, I am newly qualified with ~1 year experience and this is my first post here. It's a question that's stumped me because I'm not sure how to provide RCD protection here due to the arrangement of supplies going to the consumer unit. I will provide information below but please correct me if I'm wrong.

Context:

Its a top floor flat of a complex and there are two supplies feeding the consumer unit coming from the electrical riser which is around 10-15m from the flat itself. The supplies to the two main switches are as follows: main switch (a) is peak supply and main switch (b) is off peak. BOTH line conductor tails emerge from a single meter and as far as I know this is ok as some meters can be dual tariffs.

I have included photos of the arrangement of the supply meter, supplier isolator and tails along with a photo of the inside of the consumer unit. Unfortunately I didn't manage to get a photo of the additional switchgear located in the riser cupboard (to the left of the meter) and I don't know what it is called. Instead I have drawn (tried to the best of my ability) the wiring arrangement and what this switchgear looked like.

Problem:

As the diagram and photos show, the peak and off peak line conductors enter the consumer unit and feed their respective main switches and then final circuits fed accordingly. The issue is that there is a single neutral tail feeding the peak main switch and then a branch of conductor is fed from incoming main switch (a) to incoming main switch (b) as the neutral branch (shown as black wire in both photo and diagram).

I am not sure where to place an RCD across this installation to provide RCD protection to the sockets and luminaires at a very minimum to comply with regs.

If I have a front end RCD (not ideal) then this will trip when the off peak supply kicks in because the vector sum of current IN and current OUT will be imbalanced by the shared neutral.

I'm a little stumped and any information or advice would be really helpful. Thanks in advance.
Thinking outside the box here. I am alarmed that the off peak has no isolator switch for a start.
Would it be far simpler to get the BOARD to fit a new Two rate Meter with just the one supply out.?
An RCD on each supply should be OK with the shared Neutral as in fact it is one and the same Neutral anyway, just expensive fitting Two additional protection RCDs.
RCBOs would be the best way to go, but would involve a total rebuild.
And how do you safely isolate the off peak to work on it.? Technically you should not unless you can totally disconnect the off peak first.
Ring the DNO and ask advice.
David in Lincolnshire (retired).
 
Thinking outside the box here. I am alarmed that the off peak has no isolator switch for a start.
Would it be far simpler to get the BOARD to fit a new Two rate Meter with just the one supply out.?
An RCD on each supply should be OK with the shared Neutral as in fact it is one and the same Neutral anyway, just expensive fitting Two additional protection RCDs.
RCBOs would be the best way to go, but would involve a total rebuild.
And how do you safely isolate the off peak to work on it.? Technically you should not unless you can totally disconnect the off peak first.
Ring the DNO and ask advice.
David in Lincolnshire (retired).
Thank you for the response. I will look to contact the DNO for advice
 