Hi everyone,
I've put in an outdoor armoured cable as a spur off the ring main for a friend. This is for a pond pump and LED lighting for the pond. Thought it would be a good idea to protect the spur with a 10A 30mA type A RCBO. All working fine except for when I test the RCBO it does indeed go off but also the RCCB protecting the ring in the consumer unit also goes off. We were hoping only the spur's RCD would go off as my friend is worried that the filter on the pump will block while he's on holiday and it will trip everything in the house (including the fridge) while he's on holiday. He's consumer unit is tiny and only has one RCCB.
Any suggestions gratefully received?
I've put in an outdoor armoured cable as a spur off the ring main for a friend. This is for a pond pump and LED lighting for the pond. Thought it would be a good idea to protect the spur with a 10A 30mA type A RCBO. All working fine except for when I test the RCBO it does indeed go off but also the RCCB protecting the ring in the consumer unit also goes off. We were hoping only the spur's RCD would go off as my friend is worried that the filter on the pump will block while he's on holiday and it will trip everything in the house (including the fridge) while he's on holiday. He's consumer unit is tiny and only has one RCCB.