Ellsa100

DIY
Reaction score
5
Hi there

I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking this is whether I can safely add new plug sockets off an existing 3A fused spur (I plan to only use these plug sockets for low power devices).

The current 3A fused spur is connected to a Heatmiser wiring centre which controls our wet underfloor heating system. The wiring diagram of the Heatmiser wiring centre is below and my queries relate to the yellow highlighted sections.

1. Given Power (P) = Current (I) x Volt (V), if the power consumption is 7W and the supply voltage is 230V, wouldn't that mean the current the unit consumes is 0.03A (i.e. 7/230) or, if not, please can someone explain?

2. If I am correct in concluding the current consumed is 0.03A, why is there (a) a 3A mains supply fuse (this is in a 3A fused spur) and (b) a 5A fuse on the board? How much 'excess' fuse capacity is on the 3A fuse if the Heatmiser wiring centre is the only device connected to it?

3. If I am correct in concluding the current consumed by the Heatmiser wiring centre is 0.03A, how can the max load on the different boiler/H/W/zone outputs be 3A 230V with a max total load of 5A?

4. Would it be safe to run a couple of plug sockets coming off the 3A fused spur (I would want to use low power devices)? If so, how much spare "ampage" should there be for those plug sockets (would it, for example, be 3A less 0.03A)?

Thank you in advance
1672259599905.png
 
No, don't add sockets to the load side of the isolator for your heating.

There's many reasons for this including that any fault on anything plugged into the sockets will leave you without heating.
Anything plugged in which overloads the 3A fuse will leave you without heating.

A 3A fuse is installed because it is the nearest standard sized fuse to the load current of the system, and it is adequate to protect the cables used.

A 3A fuse also allows for any inrush currents in the system.
 
Thanks.

I think the current 3A fuses spur is off the ring main.

Could I split the spurs into two fused spurs, each of 3A? So one of the 3A fused spurs connects to Heatmiser, the other 3A fused spur connects to some plug sockets? Would I need the total power of all plugs connected to a 3A fused plug socket to be less than 230 x 3 = 690 watts (ie volt x current)?

Thanks again
 
1. That calculation is correct for a resistive load but does not take into account power factor of inductive or capacitive loads. Some devices, e.g. the pump, will take more current that P/V would suggest, up to 50% more in some cases.

2. The Heatmiser control centre itself only uses 7W, but it feeds other devices like pump(s) that consume more. The 5A fuse protects the tracks on the PCB in the Heatmiser against burnout if something like the pump short-circuits, and some fool has put a 13A fuse in the fused connection unit (i.e. spur box, FCU.) An advantage of using a 3A fuse in the FCU is that this is likely to fail first in the event of a fault vs. the internal 5A, and it is easier to replace than the internal one.

3. The individual outputs are controlled by relays each of which has a maximum rating of 3A. This is enough for the entire system but as it happens the internal wiring of the control centre is physically capable of carrying 5A. It has a safety margin when protected by the recommended 3A fuse in the spur. I agree it is a little inconsistent to recommend the 3A fuse for a device capable of handling 5A, but note the last part of answer 2 above.

4. As per @davesparks above, the FCU is required as a means of isolation for the heating system and should not be interfered with. Whether it is permissible to add another spur to feed socket outlets will depend on the configuration of the circuit, whether the FCU is a point in the ring or a spur from it. It would be non-standard to limit a socket-outlet to 3A and probably unnecessary - a 13A fused spur would be more satisfactory.
 
1. That calculation is correct for a resistive load but does not take into account power factor of inductive or capacitive loads. Some devices, e.g. the pump, will take more current that P/V would suggest, up to 50% more in some cases.

2. The Heatmiser control centre itself only uses 7W, but it feeds other devices like pump(s) that consume more. The 5A fuse protects the tracks on the PCB in the Heatmiser against burnout if something like the pump short-circuits, and some fool has put a 13A fuse in the fused connection unit (i.e. spur box, FCU.) An advantage of using a 3A fuse in the FCU is that this is likely to fail first in the event of a fault vs. the internal 5A, and it is easier to replace than the internal one.

3. The individual outputs are controlled by relays each of which has a maximum rating of 3A. This is enough for the entire system but as it happens the internal wiring of the control centre is physically capable of carrying 5A. It has a safety margin when protected by the recommended 3A fuse in the spur. I agree it is a little inconsistent to recommend the 3A fuse for a device capable of handling 5A, but note the last part of answer 2 above.

4. As per @davesparks above, the FCU is required as a means of isolation for the heating system and should not be interfered with. Whether it is permissible to add another spur to feed socket outlets will depend on the configuration of the circuit, whether the FCU is a point in the ring or a spur from it. It would be non-standard to limit a socket-outlet to 3A and probably unnecessary - a 13A fused spur would be more satisfactory.
Thanks, this is super helpful and makes sense.
 

Reply to How to understand power ratings and interaction with fuses in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, quick question. How do FCU's work? Do they just protect the load side and what I mean is, say you have a ring final with 2.5mm^2 protected by...
Replies
9
Views
1K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
621
I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
426
Hi there. I have noticed that most laptop power supply cables have a 5A fuse in the plug, but a 2.5A rating on the clover leaf end of the cable...
Replies
9
Views
2K
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock