Octopus

Customer is having an extension. In the extension, wet under floor heating to 3 zones is being installed.

The GSR says he wants a plug adjacent to the manifold .......... and he will plug the manifold etc into that.

This means the boiler will have 2 supplies..........

Do you.....
 
Am I right in saying they will be 3 zone valves for the zones controlled by individual room stats?
I’m a bit lost to the purpose of the socket.


Edit to supply the pump etc on the manifold.
If he insists then you have to provide appropriate warning labels.
Insist it should be supplied from the same circuit.
 
Last edited:
I would never have two supplies to a heating system but seen it done many times by the wet trade!!!
As far as i would be concerned you need perm L, switched L, N &E which you obviously know. There might be a switchable /triple pole and earth socket out there for them to plug into at a later date :)
 
Are the manifold and valves actually going to be switching the boiler or just opening and closing on demand from the thermostats when the existing heating is running?
 
All you are doing is outlining the 3rd option on the poll
No I'm not, IMO there should be 4 options. If I was responsible for wiring in the S/L then I would provide a 3core and earth and terminate it into a triple pole isolator at the new manifold position. If I wasn't responsible for providing the SL then I would do as he asks but explain to the plumber/person in charge of the job my reservations.
 
Some GSR are arrogant, id raise my concerns with the GSR, and customer. At the end of the day if hes connecting it its his problem.

The heating controls should be on the same circuit however if hes intending using a different circuit for the UFH and manifold zone valves he could use the trigger wires from the valves to operate a relay that pulls in the heating control circuit that way the boiler is only controlled by one circuit, and the manifold is a completely seperate.

Does a GSR have the technical ability to do this ? If he doesnt want to listen to advise maybe he does, maybe hes going to do it through a RF relay.

Much easier to keep it on same circuit IMO.
 
Customer is having an extension. In the extension, wet under floor heating to 3 zones is being installed.

The GSR says he wants a plug adjacent to the manifold .......... and he will plug the manifold etc into that.

This means the boiler will have 2 supplies..........

Do you.....

Are you sure you two are not at cross purposes, and he wants a socket instead of FCU, and he assumes you'll just feed it from the wiring centre.

I sense your being a bit touchy of late Murdoch? Perhaps another holiday in the States will calm your nerves :)
 
Are you sure you two are not at cross purposes, and he wants a socket instead of FCU, and he assumes you'll just feed it from the wiring centre.

I sense your being a bit touchy of late Murdoch? Perhaps another holiday in the States will calm your nerves :)
u wot m8?

images.jpg
 
Basically I told him that having 2 supplies into a boiler central heating system wasn’t a good idea ...... I guess Poland have different rules.

I doing the 3rd option
 
There’s not enough information in the OP.
What type of output is there from the underfloor heating controls to signal the boiler?
If it is just a pair of volt free contacts/relay output as most seem to be these days then the underfloor heating system can be fed from a separate supply with just a L & S/L link to the heating controls.
 
Well, i have just wired 7 manifolds, using in effect 7 individual supplies. The GSHP and circulation pump also have individual supplies, so thats 11 different supplies if i count them all up including TP and SP supply for GSHP and FSU supply for controller... lol
Put that in your pipe and smoke it..... ha ha
having said that there is no direct electrical interconnections as such as they are on a comms bus.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
How would you do this ....................
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
23
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Octopus,
Last reply from
plugsandsparks,
Replies
23
Views
1,562

Advert

Back
Top