Does the hot tank have 2 elements, 1 for E7 and 1 for boost?
If not does the hot water get hot over night when E7 is on?
 
Saw on that cowboy trap program on bbc1 last week, a couple in scotland got shafted by a polish builder - apart from his appauling workmanship and lack of understanding for the building regs...he had a translater go around every job with him in the van so he could communicate.

Without getting onto the foreign workers in our country debate, the one thing i think we can all agree on is - If they're working in our country, especially S/E learn the bloody language.

If they can't speak the lingo, why do people let them do work on their houses????
 
If the stat was corroded the element is leaking and needs changing.

If you disconnect the live from the stat to the element and it stops going Boooom, then it's the element, no I.R testing required.
 
If the stat was corroded the element is leaking and needs changing.

If you disconnect the live from the stat to the element and it stops going Boooom, then it's the element, no I.R testing required.
safe isolation testing required though.....
assuming its an electrician he should be conversant with that procedure..

otherwise its `old trusty`..

49a4e14e99429cf17489f850545e0937.jpg
 
as sherlock once said. " once you have eliminated the impossible, then the answer must be the bloody obvious". ( misquote copyrighted 11.30am, 19/01/13 )
 