Did anyone fit a Vent-axia Multivent MVDC-MSH or similar fan with 2 switch lines.
So I have bathroom and a tea point. Both of the same in-line fan. I have connected each of the independent switch lines to dedicated Sl1 and Sl2 terminals in the fan. Unfortunately when in one room lights are on then straight other room light on to troughs the Ls . If somebody knows how to correct connect that I would be greatly appreciated.
 

Attachments

  • 9966ECBA-265C-48EB-BE50-4997E103C6EC.png
    9966ECBA-265C-48EB-BE50-4997E103C6EC.png
    748.1 KB · Views: 107
The 2 inputs are separate and there should be no interlinking between SL1 and2 If there is there has to be a wiring error or a fault with the unit. IIRC the inputs are both opto isolated so any internal interlinking between the 2 should be impossible. Check your wiring carefully again.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
In-line Fan with 2 switch lines
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Kinxsize,
Last reply from
freddo,
Replies
1
Views
482

Advert